Greg, Maybe your AHJ is looking at NFPA 75, Standard for the Protection of Information Technology Equipment, 2003 Edition for his guidance on what is acceptable. NFPA 75 is pretty clear in 8.1.1 and 8.1.1.1.
Chapter 8 Fire Protection and Detection Equipment 8.1 Automatic Sprinkler Systems. 8.1.1 Information technology equipment rooms and information technology equipment areas located in a sprinklered building shall be provided with an automatic sprinkler system. 8.1.1.1 Information technology equipment rooms and information technology equipment areas located in a non-sprinklered building shall be provided with an automatic sprinkler system or a gaseous clean agent extinguishing system or both (see Section 8.4). 8.1.1.2* Either an automatic sprinkler system, carbon dioxide extinguishing system, or inert agent fire extinguishing system for the protection of the area below the raised floor in a information technology equipment room or information technology equipment area shall be provided. 8.1.2* Automatic sprinkler systems protecting information technology equipment rooms or information technology equipment areas shall be installed in accordance with NFPA 13, Standard for the Installation of Sprinkler Systems. 8.1.3 Sprinkler systems protecting information technology equipment areas shall be valved separately from other sprinkler systems. 8.1.4* Automated Information Storage System (AISS) units containing combustible media with an aggregate storage capacity of more than 0.76 m3 (27 ft3) shall be protected within each unit by an automatic sprinkler system or a gaseous agent extinguishing system with extended discharge. 8.1.5 Automatic sprinkler systems protecting information technology equipment rooms or information technology equipment areas shall be maintained in accordance with NFPA 25, Standard for the Inspection, Testing, and Maintenance of Water-Based Fire Protection Systems. David David L. Powell Fire Protection Officer LES P.O. Box 1789 (all mail) 1305 Avenue I Eunice, NM 88231 Tel: +01 505 394 6021 Mob: +01 505 602 0382 Email: [EMAIL PROTECTED] Web: www.nefnm.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Tuesday, April 08, 2008 10:11 AM To: [email protected] Subject: fm200 vs sprinkerls We have done multiple projects in which the server rooms have been protected with FM200 systems and had no sprinklers. We now have a bldg like this in which the AHJ is stating that a room with FM200 is not exempted from NFPA 13's requirement to be protected throughout and therefore must have both FM200 and sprinklers. Is this a true statement in you other AHJ's eyes? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Monday, April 07, 2008 6:48 AM To: [email protected] Subject: Fitter Question Maybe more suited for chat but I'll throw it out here. I need to get an in-place groover for an upcoming job. I've borrowed a friends rigid before but it's gone. Can any fitters share their likes and dislikes? Rigid vs. Reed, or others... I wish they made one for a 700 as I have to groove old 4" and 6" sch. 40. I've got to cut-in about 12 FCV's 8-10' in the air. All recommendations and advice accepted. (I don't like roustabouts) Tom GRS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) DISCLAIMER: This email transmission is confidential Louisiana Energy Services, L.P and intended solely for the person or organization to which it is addressed. If you are not the intended recipient, you must not copy, distribute or disseminate the information or take any action in reliance of it. Any views expressed in this message are those of the individual sender, except where the sender specifically states them to be the views of any organization or employer. If you have received this message in error, do not open any attachment but please notify the sender (above) and delete this message from your system. Please rely on your own virus check, as no responsibility is taken by the sender for any damage arising out of any bug or virus. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)