Greg,

Maybe your AHJ is looking at NFPA 75, Standard for the Protection of
Information Technology Equipment, 2003 Edition for his guidance on what
is acceptable.  NFPA 75 is pretty clear in 8.1.1 and 8.1.1.1.

Chapter 8 Fire Protection and Detection Equipment
8.1 Automatic Sprinkler Systems.
8.1.1  Information technology equipment rooms and information technology
equipment areas located in a sprinklered building shall be provided with
an automatic sprinkler system.
8.1.1.1  Information technology equipment rooms and information
technology equipment areas located in a non-sprinklered building shall
be provided with an automatic sprinkler system or a gaseous clean agent
extinguishing system or both (see Section  8.4).
8.1.1.2*  Either an automatic sprinkler system, carbon dioxide
extinguishing system, or inert agent fire extinguishing system for the
protection of the area below the raised floor in a information
technology equipment room or information technology equipment area shall
be provided.
8.1.2*  Automatic sprinkler systems protecting information technology
equipment rooms or information technology equipment areas shall be
installed in accordance with  NFPA 13, Standard for the Installation of
Sprinkler Systems.
8.1.3  Sprinkler systems protecting information technology equipment
areas shall be valved separately from other sprinkler systems.
8.1.4*  Automated Information Storage System (AISS) units containing
combustible media with an aggregate storage capacity of more than 0.76
m3 (27 ft3) shall be protected within each unit by an automatic
sprinkler system or a gaseous agent extinguishing system with extended
discharge.
8.1.5  Automatic sprinkler systems protecting information technology
equipment rooms or information technology equipment areas shall be
maintained in accordance with  NFPA 25, Standard for the Inspection,
Testing, and Maintenance of Water-Based Fire Protection Systems.

David
 
David L. Powell
Fire Protection Officer
 
LES
P.O. Box 1789 (all mail)
1305 Avenue I 
Eunice, NM 88231
 
Tel:          +01 505 394 6021
Mob:        +01 505 602 0382
Email:      [EMAIL PROTECTED]
Web:        www.nefnm.com
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, April 08, 2008 10:11 AM
To: [email protected]
Subject: fm200 vs sprinkerls

We have done multiple projects in which the server rooms have been
protected
with FM200 systems and had no sprinklers.
We now have a bldg like this in which the AHJ is stating that a room
with
FM200 is not exempted from NFPA 13's requirement to be protected
throughout
and therefore must have both FM200 and sprinklers.

Is this a true statement in you other AHJ's eyes?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Monday, April 07, 2008 6:48 AM
To: [email protected]
Subject: Fitter Question

Maybe more suited for chat but I'll throw it out here.

I need to get an in-place groover for an upcoming job.
I've borrowed a friends rigid before but it's gone.
Can any fitters share their likes and dislikes?  
Rigid vs. Reed, or others...

I wish they made one for a 700 as I have to groove old 4" and 6" sch.
40.
I've got to cut-in about 12 FCV's 8-10' in the air.
All recommendations and advice accepted.
(I don't like roustabouts)

Tom
GRS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


DISCLAIMER:
This email transmission is confidential Louisiana Energy Services, L.P and 
intended solely for the person or organization to which it is addressed. If you 
are not the intended recipient, you must not copy, distribute or disseminate 
the information or take any action in reliance of it. Any views expressed in 
this message are those of the individual sender, except where the sender 
specifically states them to be the views of any organization or employer. If 
you have received this message in error, do not open any attachment but please 
notify the sender (above) and delete this message from your system. Please rely 
on your own virus check, as no responsibility is taken by the sender for any 
damage arising out of any bug or virus.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to