Yes he is factual.  The deal is that for some, FM 200 is NOT a
substitute unless there is a backup system or other provisions have been
made to protect the owner from total loss of their data systems.  Some
of this also depends on the value of the data center and it's impact on
production interruption. 

In a recent discussion with an Underwriter and AHJ the fact that while
the FM 200 would most likely extinguish any fire related to the
equipment, it may not be suitable for the other combustibles that often
makeup these types of rooms.  Those other combustibles being furniture,
paper products, plastics for various media, etc.  A "one shot" system
leaves the owner vulnerable if there was a reflash.  So the answer has
been to require sprinklers in either wet or pre-action format as the
backup system.  

In the scope of the IFC it states that "...Automatic fire extinguishing
systems shall not be considered alternatives for the purpose of
exceptions or reductions permitted by other requirements of this code."
NFPA 13 has similar words where it comes down to the approval of the
AHJ.

So the alternative may or may not be accepted as an alternative by the
AHJ.  He has the final say so.

When the code says sprinkled throughout, some see no exceptions to that,
period and in some case that isn't a bad thing.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Tuesday, April 08, 2008 12:11 PM
To: [email protected]
Subject: fm200 vs sprinkerls

We have done multiple projects in which the server rooms have been
protected with FM200 systems and had no sprinklers.
We now have a bldg like this in which the AHJ is stating that a room
with FM200 is not exempted from NFPA 13's requirement to be protected
throughout and therefore must have both FM200 and sprinklers.

Is this a true statement in you other AHJ's eyes?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Monday, April 07, 2008 6:48 AM
To: [email protected]
Subject: Fitter Question

Maybe more suited for chat but I'll throw it out here.

I need to get an in-place groover for an upcoming job.
I've borrowed a friends rigid before but it's gone.
Can any fitters share their likes and dislikes?  
Rigid vs. Reed, or others...

I wish they made one for a 700 as I have to groove old 4" and 6" sch.
40.
I've got to cut-in about 12 FCV's 8-10' in the air.
All recommendations and advice accepted.
(I don't like roustabouts)

Tom
GRS
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to