Yes he is factual. The deal is that for some, FM 200 is NOT a substitute unless there is a backup system or other provisions have been made to protect the owner from total loss of their data systems. Some of this also depends on the value of the data center and it's impact on production interruption.
In a recent discussion with an Underwriter and AHJ the fact that while the FM 200 would most likely extinguish any fire related to the equipment, it may not be suitable for the other combustibles that often makeup these types of rooms. Those other combustibles being furniture, paper products, plastics for various media, etc. A "one shot" system leaves the owner vulnerable if there was a reflash. So the answer has been to require sprinklers in either wet or pre-action format as the backup system. In the scope of the IFC it states that "...Automatic fire extinguishing systems shall not be considered alternatives for the purpose of exceptions or reductions permitted by other requirements of this code." NFPA 13 has similar words where it comes down to the approval of the AHJ. So the alternative may or may not be accepted as an alternative by the AHJ. He has the final say so. When the code says sprinkled throughout, some see no exceptions to that, period and in some case that isn't a bad thing. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Tuesday, April 08, 2008 12:11 PM To: [email protected] Subject: fm200 vs sprinkerls We have done multiple projects in which the server rooms have been protected with FM200 systems and had no sprinklers. We now have a bldg like this in which the AHJ is stating that a room with FM200 is not exempted from NFPA 13's requirement to be protected throughout and therefore must have both FM200 and sprinklers. Is this a true statement in you other AHJ's eyes? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Monday, April 07, 2008 6:48 AM To: [email protected] Subject: Fitter Question Maybe more suited for chat but I'll throw it out here. I need to get an in-place groover for an upcoming job. I've borrowed a friends rigid before but it's gone. Can any fitters share their likes and dislikes? Rigid vs. Reed, or others... I wish they made one for a 700 as I have to groove old 4" and 6" sch. 40. I've got to cut-in about 12 FCV's 8-10' in the air. All recommendations and advice accepted. (I don't like roustabouts) Tom GRS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)