Probably, but not for the reason stated, see IFC '03 904.2.  If you don't
put the sprinklers in it's an unsprinklered building for all matters that
relate to sprinklers exceptions.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Tuesday, April 08, 2008 11:11 AM
To: [email protected]
Subject: fm200 vs sprinkerls

We have done multiple projects in which the server rooms have been protected
with FM200 systems and had no sprinklers.
We now have a bldg like this in which the AHJ is stating that a room with
FM200 is not exempted from NFPA 13's requirement to be protected throughout
and therefore must have both FM200 and sprinklers.

Is this a true statement in you other AHJ's eyes?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852