Greg, It is true for the Eugene area.
The IFC 903.1.1 allows alternative systems under specific conditions and AHJ approval. IFC 903.3.1.1.1 Has exempt locations (rooms or areas) but those locations must be equipped with an auto fire detection system. There are 4 specific criteria; 1) where the application of water constitutes a serious life or fire hazard, 2) where sprinklers are considered undesirable due to nature of contents and approved by AHJ, 3) generator and transformer rooms separated from rest of building by 2 hr fire-resistive construction, 4) rooms/areas are of noncombustible construction with wholly noncombustible contents. Also, an alternate system like FM200 is a one shot only application,which does not meet the intent of an Alternate Materials & Method approach, as described in IFC 104.9, that requires the alternate to be equivalent to the orginal protection. Sprinklers are a continuous application. Mike Thrapp Fire Marshal Eugene, OR 97401 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Tuesday, April 08, 2008 09:11 To: [email protected] Subject: fm200 vs sprinkerls We have done multiple projects in which the server rooms have been protected with FM200 systems and had no sprinklers. We now have a bldg like this in which the AHJ is stating that a room with FM200 is not exempted from NFPA 13's requirement to be protected throughout and therefore must have both FM200 and sprinklers. Is this a true statement in you other AHJ's eyes? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross Sent: Monday, April 07, 2008 6:48 AM To: [email protected] Subject: Fitter Question Maybe more suited for chat but I'll throw it out here. I need to get an in-place groover for an upcoming job. I've borrowed a friends rigid before but it's gone. Can any fitters share their likes and dislikes? Rigid vs. Reed, or others... I wish they made one for a 700 as I have to groove old 4" and 6" sch. 40. I've got to cut-in about 12 FCV's 8-10' in the air. All recommendations and advice accepted. (I don't like roustabouts) Tom GRS _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)