I believe a 1/2" sheet of gyp bd meets this criteria but you may want to
show him 13R (07)6.9.2.
The requirement for the thermal barrier has been removed. 
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, April 11, 2008 6:04 AM
To: [email protected]
Subject: thermal barrier

NFPA 13R includes an exclusion for sprinklers in bathrooms less than
55 sqft and where the walls behind fixtures "are of non-combustible or
limited combustible materials providing a 15-minute thermal barrier". Is
there any way to quantify if this criteria is met? A thermal barrier to
what? I have an AHJ questioning this.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut