Don't forget the thermal barrier is required behind the fixtures and must 
extend to the floor even behind the bathtubs. If you need to prove the rating 
(15min) a simple spec sheet on gypsum board should provide that. Any UL fire 
rating details will show ½" gypsum on each side of a metal stud wall as at 
least one-hour. 

Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez
Sent: Friday, April 11, 2008 7:35 AM
To: [email protected]
Subject: RE: thermal barrier

I believe a 1/2" sheet of gyp bd meets this criteria but you may want to show 
him 13R (07)6.9.2.
The requirement for the thermal barrier has been removed. 
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC
Sent: Friday, April 11, 2008 6:04 AM
To: [email protected]
Subject: thermal barrier

NFPA 13R includes an exclusion for sprinklers in bathrooms less than
55 sqft and where the walls behind fixtures "are of non-combustible or limited 
combustible materials providing a 15-minute thermal barrier". Is there any way 
to quantify if this criteria is met? A thermal barrier to what? I have an AHJ 
questioning this.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)