Double check that, usually you need "Type X" 5/8" to achieve the 1 hr. rating.  
According to the IBC it takes two layers, staggered of 1/2" each side to get a 
1 hour rating.  See Item 14-1.2 in Table 719.1(2).  One layer of 5/8" Type X on 
each side will also give 1hr, Item 14-1.3.

You will most likely be within the 15 minute window with standard 1/2" sheet 
rock over studs with no exposed combustibles.  Make sure all penetrations into 
the stud cavity are sealed with fire caulk.

Thermal barrier is between the bathroom and the adjacent space.  


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Eric Tysinger
Sent: Friday, April 11, 2008 8:47 AM
To: [email protected]
Subject: RE: thermal barrier

Don't forget the thermal barrier is required behind the fixtures and must 
extend to the floor even behind the bathtubs. If you need to prove the rating 
(15min) a simple spec sheet on gypsum board should provide that. Any UL fire 
rating details will show ½" gypsum on each side of a metal stud wall as at 
least one-hour. 

Eric Tysinger
Design Manager
Wayne Automatic Fire Sprinklers, Inc.


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Dewayne Martinez
Sent: Friday, April 11, 2008 7:35 AM
To: [email protected]
Subject: RE: thermal barrier

I believe a 1/2" sheet of gyp bd meets this criteria but you may want to show 
him 13R (07)6.9.2.
The requirement for the thermal barrier has been removed. 
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC
Sent: Friday, April 11, 2008 6:04 AM
To: [email protected]
Subject: thermal barrier

NFPA 13R includes an exclusion for sprinklers in bathrooms less than
55 sqft and where the walls behind fixtures "are of non-combustible or limited 
combustible materials providing a 15-minute thermal barrier". Is there any way 
to quantify if this criteria is met? A thermal barrier to what? I have an AHJ 
questioning this.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to