Todd, Take a look at 2006 IBC Table 721.2.1.4(2) "Finish Material" 1/2" GWB = 15 Minutes.
Hope that helps. John Drucker Fire Protection Subcode Official (AHJ) -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Friday, April 11, 2008 7:04 AM To: [email protected] Subject: thermal barrier NFPA 13R includes an exclusion for sprinklers in bathrooms less than 55 sqft and where the walls behind fixtures "are of non-combustible or limited combustible materials providing a 15-minute thermal barrier". Is there any way to quantify if this criteria is met? A thermal barrier to what? I have an AHJ questioning this. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)