There will be more multi purpose systems on the market soon, along with
different trades doing the installation.  As Mike said earlier, some
states don't have licensing requirements.  Georgia regulates all systems
except one and two family installations.  Maybe the combination of new
systems and new installers should require the bucket test to at least
prove the correct flow from one or two sprinklers.
 
If the Residential Building Code (or Plumbing Code or whatever) is
modified to incorporate some type of hybrid system other than a 13D (and
it appears it will), would a TIA to 13D have any affect on the
Residential or Plumbing Code?   Wouldn't the bucket test need to be
adopted into these other codes?

Some years ago there was a small orifice residential (was it K=2.8?).  I
believe there was a recall on sprinklers by the manufacturer, but before
the recall we installed this model in a residential complex, I believe
the systems were 13D modified by the local authority, and the bucket
test was required.  It failed.  The pre design and post installation
water test were the same, so maybe the problem was in the 1-1/2" UG, we
don't know.  What did work was to change the sprinklers to a larger
orifice residential model.  We found the fix to the problem after the
first two units then all the rest worked fine.
 
I don't like the aggravation and cost of the bucket test but it does
appear to provide more definitive proof if the system will work.  On the
above project the calculations were checked and rechecked with the small
orifice sprinkler and found to be correct.  Without the bucket test the
sprinklers would have only flowed about half of what was required.

Bobby McCullough

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Tuesday, April 15, 2008 11:57 AM
To: [email protected]
Subject: RE: What is a Bucket Test? (TIA Needed)

Thanks Mike,

I understand the concept, however what if a) the job is installed to
plan & calcs b) the job is installed to revised plans & calcs. ?  What
I'm getting at is the need for the bucket test if the plans and calcs
demonstrate compliance.  


What I'm getting at is just how reliable are hydraulic calcs  ? On the
surface the bucket test implies that hydraulic calculations in of
themselves are not to be relied on and that proof of hydraulic
performance is neccesary. If that's the case how about 13R and 13
Systems ?.   Its not a water supply "connection" issue since a main
drain test is the accepted method to validate this. While the bucket
test also performs this function, the need to measure performance in the
area of operation serves no other purpose then to validate hydraulic
design. If it's the installation, i.e. obstructions, pipe size,
sprinkler heads we're concerned about we need to be flow testing beyond
the area of operation. 

Lastly theres nothing in our adopted codes or standards that require a
"bucket test". Frankly a contractor would well be within their right to
appeal my decision to require such a test.  Don't take that as I don't
believe theres some validity to "bucket tests", I do, but theres nothing
for me to hang my enforcement hat on and we all know how contractors
insist on "show me in the code."

Sincerely,

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

Safe Buildings Save Lives ! 

 