Karen, If I understand you correctly, you have 2 levels of apartments @ 10-10 and one penthouse on top of that. If you truly have a basement, it doesn't sound like you need standpipes. I believe the requirement for standpipes is "more than 30' to the highest occupied floor" and this is measured from fire department access. Unless they can drive up to the building and come in thru the basement, you only have 21'-8" to the floor level of the third floor.
If I missed something in your description, please say so. I'm not running on all cylinders today. Cliff Whitfield, SET Fire Design, Inc. -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent: Monday, April 21, 2008 1:00 PM To: [email protected] Subject: Help with standpipe I have a 13R building that has a basement below street level, two floors with apartments and a penthouse that takes up entire third floor. Each floor is 10'10" finished floor to finished floor. I know that because of the 30' rule I have to have a standpipe. My problem is how. The building is an old building being renovated and there is one staircase in the lobby. These stairs serve two apartments each. The stairs leading up to the penthouse is totally enclosed with a door at the second floor. Does this still qualify for a standpipe and if so do I take it all the way through the penthouse to the roof. The building will be completely sprinklered. Also does the standpipe need to go to the basement as well? There are no apartments there but is being used for mechanical equipment and storage. Karen Purvis Designer Facility Systems Consultants 714 S Gay St Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)