I haven't figured out why yet, but I still am not able to reply back to the
forum.  So, thanks for everyone's input.  The TYCO data that many pointed me
to is good only for recessed and flush sprinklers not concealed.  The other
issue that I'm running into is the minimum distance between beams.  The ones
on this project are between 2'8" to 3'3" o.c. while TYCO stipulates a min of
3'4".  So now we are suggesting that the beams be spaced differently and
that we be given a variance to use recessed heads in these rooms then we can
use the beam criteria.  I was just hoping to find some other approach that
would allow the concealed heads.