Never worry about the AHJ's insurance, they don't need it. As far as ours
goes, what is outside the scope of 13D, and is approved by the AHJ, is all
we really need.(Or at least the best we can hope for.) Just like those pesky
10/12, 12/12, 16/12 beamed sloped ceilings, sauna's, elevators, elevator
equipment rooms, or the two thousand other things 13D never considered in
residences. Basically unless a new listing procedure has been accepted,
anything but a flat smooth ceiling is outside the listing of residential
heads. I don't know what deal the mfg's use to list for 4/12 or 8/12, but
it's not an actual test, I believe its just an interpolation of
data.(Someone correct me if I'm wrong?)

The Insurance companies money was meant to be spent somewhere, if not then
our premiums would be a lot less.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Mike Brown (TECH- GVL)" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, May 06, 2008 12:58 PM
Subject: RE: Residential Sprinklers and Beam Obstructions


The NFPA 13D Committee in their wisdom (or as some people have suggested
lack thereof) put in the 2007 Edition Paragraph 8.1.3.1.2

"Where construction features or other special conditions exist that are
outside the scope of sprinkler listings, listed sprinklers shall be
permitted to be installed beyond their listing limitations."


I hope that you and the AHJ have good insurance or a lot of money.

Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, May 06, 2008 2:03 PM
To: [email protected]
Subject: Re: Residential Sprinklers and Beam Obstructions

Bob:

We run into this all the time. First question are the beams structural? If
the beams are decorative only drill the beams use your concealed heads and
space as normal. While the beam rules for TYCO are ok, they have a lot of
situations where you would have to tell the Arch. how to layout the beams
before hand.(Like that's ever going to happen!) If you read the white paper
for slope Beam ceilings exceeding 8/12 you'll see that the concealed
sprinklers responded slightly better when in the beams than in the pockets.
If this is true on a steep slope ceiling it should be reasonable to apply it
to flat beam ceilings. (With heads in the beams less than 12" below the
actual flat ceiling, we usually use the flows for 8/12 slope to offset any
delay for the lower position of the heads,) All our AHJ's are OK with this.

If your beams are structural, good luck getting the Arch. or Structural Eng.
to let you put a 21/2" hole vertically thru a structural member. Then we
usually end up with heads in every pocket, because you can't center a head
and still get far enough away from the beams to spray under them.

Good Luck!
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Bob Knight" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, May 06, 2008 10:51 AM
Subject: Residential Sprinklers and Beam Obstructions


I'm working on a home (13D) that has several rooms with the ceiling broken
up by "beam pockets".  These vary in width from 2'8" to 3'3" o.c. with the
beams being 6" deep.  Concealed residential sprinklers are being used.  In
one room, which is 224 sf, if I place a sprinkler in every pocket like I
think I should, there will be 13 sprinklers.  This averages out to 17 sf
per
head.  Another room is 375 sf and will require 10 sprinklers.  This
averages
at 37.5 per head.  In rooms of this size do I really need a sprinkler in
every pocket?  Can a sprinkler be placed in every other pocket and be
acceptable?  Has anyone else found a better way to protect rooms like
this?
Any and all suggestions will help.

Thanks,

Bob Knight, CET
(208) 318-3057
[EMAIL PROTECTED]
www.firebyknight.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to