IPA:

Could not disagree more strenuously, though I really like your beer.   

How many sprinklers are we calculating in this compartment?   How many
do we reasonably expect to operate in case of a fire?  It was described
that the beams are only 6" deep; combustion byproduct will move pretty
efficiently over those bumps and there is no way to be sure if
sprinklers would operate over the fire or if they would skip to the
other side of the room.   There are potentially 13 sprinklers in the
room and 4 or 5 or more could easily operate, none of which would be
flowing at the designed pressure or flow rate.

I think it's a much better approach to use sprinklers on the beams as
discussed, or sidewalls, and protect the room with the fewest number of
sprinklers that comply with the design criteria, for reasons of
aesthetics, cost-efficiency and hydraulics.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of IPA
Sent: Tuesday, May 06, 2008 5:18 PM
To: [email protected]
Subject: Re: Residential Sprinklers and Beam Obstructions

Sometimes, no matter how ridiculous it seems, it's better to just to
install
them in every pocket then at least you're covered liability wise. Also,
when
you get into these high dollar luxury homes with beams, slopes,
fireplaces
in every room etc.. aesthetics plays a very important role and the
homeowner
will usually want a ton of flat plate concealed sprinklers VS. four
'uglies'
sticking out of the beams. I can't say I'd blame them when forking over
large amounts of money just to have the ugliest sprinklers on the market
installed in the most conspicuous places in the most extravagant rooms
in
the house.....



On 5/6/08, Bob Knight <[EMAIL PROTECTED]> wrote:
>
> I'm working on a home (13D) that has several rooms with the ceiling
broken
> up by "beam pockets".  These vary in width from 2'8" to 3'3" o.c. with
the
> beams being 6" deep.  Concealed residential sprinklers are being used.
In
> one room, which is 224 sf, if I place a sprinkler in every pocket like
I
> think I should, there will be 13 sprinklers.  This averages out to 17
sf
> per
> head.  Another room is 375 sf and will require 10 sprinklers.  This
> averages
> at 37.5 per head.  In rooms of this size do I really need a sprinkler
in
> every pocket?  Can a sprinkler be placed in every other pocket and be
> acceptable?  Has anyone else found a better way to protect rooms like
> this?
> Any and all suggestions will help.
>
> Thanks,
>
> Bob Knight, CET
> (208) 318-3057
> [EMAIL PROTECTED]
> www.firebyknight.com
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@
firesprinkler.org>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to