Sorry, CRU is commercial rental unit. The corridor sprinkler has to cover up to the lease line. So for all practical purposes, it could be considered that there was a wall at the lease line, and the valence was protruding out from that wall. Will the valence be an obstruction (per NFPA 13) as it is more than 18" below the sprinklers? To exaggerate, if the ceiling was 20 feet high and the 26" wide valence was at 8 feet above the floor, would you consider the valence as a potential obstruction? This could happen if there is a shelf along the wall and the sprinkler at the ceiling level is very close to the wall.
Tony -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: June 2, 2008 1:29 PM To: [email protected] Subject: Re: Obstruction I did a tenant fit up in a mall with a similar situation a few years back. FM was the insurer. I was told that unless the obstruction rules in 13 (or 2-8N) could be met, we had to sprinkler beneath. In my situation, we sprinklered below them. (I'm assuming that CRU is commercial rental units or something similar) At 03:00 PM 6/2/2008, you wrote: >Shopping mall with CRU's on one side and mall corridor on the other. At >the lease line there is an "L" shaped valence that drops 20 inches >(vertical, at the lease line)from the ceiling and runs 26 inches >(horizontal) towards the corridor. Typically there is no wall between >the CRU's and the mall. Is this valence an obstruction to the sprinklers at the high ceiling level? > >My first solution was to space the sprinklers on both sides of the >valence (CRU side and mall side), so that they cover up to the >centre-line of the 26 inch wide valence. However, the sprinklers on the >CRU side will change for tenant renovations, and the mall owner will >not be able to enforce the tenant to provide coverage beyond the lease >line. Hence, the sprinkler in the corridor side has to cover up to the >lease line. Are the sprinklers in the corridor unobstructed due to the >valence being more than 18 inches below the sprinkler deflector, or is >the valence an obstruction, and possibly requiring sprinklers below the valence? > >Tony > > concealed sprinkler > _______ __________________I_______ceiling > I I > I I > I I <-6"-> > I I 20" > I I > I I_____________ > I I > I_________________I > > <------ 26 -------> > > > I<--- lease line > > CRU's Mall corridor > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > >To Unsubscribe, send an email >to:[EMAIL PROTECTED] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)