I was referring to the 2002 Edition of NFPA which is still adopted by a
majority of the US. 

Mark E. Eckard S.E.T.
Engineering Manager
Lowe's Companies
1605 Curtis Bridge Road
REEC Dock
Wilkesboro, N.C. 28697
Phone: (336) 658-4359
Fax: (336) 658-3257
Cell: (336) 467-0194
Email: [EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, May 28, 2008 1:14 PM
To: [email protected]
Subject: Re: Seismic Calcs

Mark,

Can you give me some background on where you've come to this conclusion 
on seismic design category D and higher not being
within the scope of NFPA-13?  My latest ASCE7 manual seems to suggest 
otherwise.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website



Eckard, Mark - Mark E wrote:
> Another issue with seismic bracing design and calculation is the fact
> that NFPA 13 only applies to seismic design category A, B, & C.
> Categories "A" and "B" usually do not require bracing unless it is a
> local jurisdictional requirement to brace everything.  Seismic design
> category D and higher are out of the scope of NFPA-13 and require
design
> by a Professional Engineer.  So in summary NFPA is good for Seismic
> design category "C".
> I have come to realize that quite a large number of designers don't
> realize this. 
>
> Mark E. Eckard S.E.T.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Steve
> Leyton
> Sent: Wednesday, May 28, 2008 11:33 AM
> To: [email protected]
> Subject: RE: Seismic Calcs
>
> If you consider this issue in terms of the 2007 standard, the
sprinkler
> system EQB designs are based on standard values that can be taken from
> referenced sources (such as ASCE).  You then plug the values into
> equations prescribed by NFPA 13 and you get a finalized design
> (basically, you confirm the fastener or means of anchorage for the
brace
> assembly).   None of which takes into account the capacity of the
> building itself to bear the applied loads that have been calculated,
but
> you don't need the help of an SE to simply design the braces.
>
> Once upon a time, we did our designs on a deferred basis, showed EQB's
> every 40', picked a hanger based on the type of structural member and
> submitted for approval.  Today, especially here in the Southwest, we
> consult the project structural engineer of record on every project.
> Modern lightweight construction systems, engineered wood products and
> high seismic force values often mean that even if one could design a
> brace assembly that bears enough load to space out to 40' on center,
you
> simply can't put 600, or 700 or 800 lbs. of horizontal load on the
floor
> or roof framing.  We currently have projects where bracing is limited
to
> 25-30' on center, just to dilute the load on each brace.
>
> Southern California has several fire departments that now REQUIRE
review
> by the SE of record and an accompanying letter of acceptance.  This
> speaks to the original question of what to put on the shop drawings -
> perhaps nothing, if you can submit documentation of a 3rd-party
review.
> I know that this is another step that most in our industry have never
> undertaken and generally doesn't account for in estimating design
costs,
> but I strongly recommend that every project be submitted to the
> Architect for review by the designer(s) of record before submittal to
> the FD.  And if you're in a region that is just now breaking into the
> whole "seismic thing", I would also craft language into my standard
> proposal form that excludes costs for review by structural engineer as
> may be required.
>
> Steve Leyton
> Protection Design & Consulting
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd
> Williams - FPDC
> Sent: Wednesday, May 28, 2008 7:51 AM
> To: [email protected]
> Subject: Re: Seismic Calcs
>
> Bill,
>
> I think that you may have discovered another disconnect between 
> theory and practice. To my knowledge, none of the AHJs in my area 
> have either the expertise or staff to do a review on seismic. My 
> guess is that they are just going to say "yes, there is seismic". 
> That is pretty much what I see now and I don't see it changing, given 
> municipal budgeting. The exception could possibly be in larger cities 
> or at the state level. The structural engineer from the design team 
> (assuming that there is one) would be the only person qualified to do 
> an actual review. Whether they ever see sprinkler shop drawings is 
> questionable.
>
>
> At 10:02 AM 5/28/2008, you wrote:
>   
>> NFPA 13-2007, 22.1.3(39) requires "Calculation of loads for sizing
and
>> details of sway bracing".  What should a typical shop drawing package
>> include so that the selected sway bracing can be approved?
>>
>> Who reviews these calculations prior to submission to the AHJ?  Do
AHJs
>> pass these on to structural design reviewers, or are the sprinkler
>> installer's submittals accepted without review?
>>
>> Bill Brooks
>>
>> William N. Brooks, P.E.
>> Brooks Fire Protection Engineering Inc.
>> 372 Wilett Drive
>> Severna Park, MD 21146
>> 410-544-3620 Phone
>> 410-544-3032 FAX
>> 412-400-6528 Cell
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email
>>     
> to:[EMAIL PROTECTED]
>   
>> (Put the word unsubscribe in the subject field)
>>     
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to