Garth,

I believe that was new to 2007, in 13, 13R and 13D. CT is using 2002. I understand that is a better arrangement, but I have been asked to address this strictly from a Code standpoint. Is there something comparable in 2002?


At 10:10 AM 6/5/2008, you wrote:
Sorry Todd, I omitted the portion I was trying to send which is
(C)  Where sidewall sprinklers are more than 3 ft (914 mm) above the top of
cabinets, the sprinkler shall be permitted to be installed on the wall above
the cabinets where the cabinets are no greater than 12 in. (305 mm) from the
wall.

the language seems to imply that less than 3' is no good.  No soffit above
the cabinets to finish off the look?

Garth
----- Original Message -----
From: "Todd Williams - FPDC" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, June 05, 2008 7:36 AM
Subject: Residential sidewall obstructions


> I got a call from a contractor this morning about a residential
> sidewall sprinkler located in a kitchen of a 13D system. The sidewall
> is located over the kitchen cabinets; it is 8" above the top of the
> cabinet and the cabinet sticks 11" out into the room from the
> sprinkler. I looked at the obstruction rules in 8.10.7 and could not
> find anything that applies to this situation. The closest thing would
> be the floor mounted obstruction requirements in section 8.10.7.2.2.
> According to those numbers, it would be OK. Am I missing something?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to