Joe,
Thanks. I would be interested in seeing that. I'm not surprised at
that, given the configuration. Would a sprinkler 3 ft above the
cabinet be more effective than one 7.5"? (I visited the site and
measured the arrangement. The sprinkler is 7.5" above the cabinet and
the deflector is 8" behind the cabinet face.).
At 10:27 AM 6/6/2008, you wrote:
Todd,
A few years back we had Tyco run a mock up of exactly what you are
describing for a 13R system and it failed the test. It was not able to
extinguish a fire on the counter top. I have the video on VHS. You can
contact me off forum if you want some more info. I know your job is 13D but
I thought I would share.
Best regards,
Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: [EMAIL PROTECTED]
Web Site: http://www.burtellfire.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Friday, June 06, 2008 5:34 AM
To: [email protected]
Subject: Residential sidewall obstructions - the sequel
I read through the commentary in the handbook for the 2007 edition of
13D regarding the obstruction created by cabinets. That said the
concern was items being stored on top of the cabinets obstructing
discharge - a legitimate concern. If the top of the cabinet was not
flat and had a slope so that items could not be stored, would that
accomplish the same thing as the 3 ft elevation difference? My
original concern in this question was the obstruction of that wall
wash part of the discharge from protecting the counter area.
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)