Haven't done any for quite a while but in the old days doing deluge
system on outdoor equipment like pumps, transformers, heaters etc... We
used structural shapes like small I Beams with plate on the bottom and a
concrete pier or if a slab available we anchored the plate to the slab.
I believe the beams we used were called 10S but I might be wrong. There
is no prescriptive code you just have to do what works.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Allan
Seidel
Sent: Saturday, June 07, 2008 10:28 AM
To: [email protected]
Subject: When all horizontal pipe hangers are supports from below

A sprinkler system, both mains and branch lines, will be supported  
entirely from below. There will be no hangers and supports will occur  
at least every ten feet. NFPA 13 does not seem to address this  
condition in any detail. I can think of many ways to support and  
anchor the piping. The problem is I need to know what methods are not  
permitted. For example, is piping strapped to a unistrut, point-load  
style, technically not permitted?

Thank you,
Allan Seidel
St. Louis, MO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to