Both K 7.9 and K 8.1 are in the same allowed range so are considered the same. You are suppose to be using the nominal K factor for both.

Roland

On Jun 19, 2008, at 1:28 AM, Aydın ÖZKAYA wrote:

Let me give some more details:

- area is approx. 2500 m2 single space
- the ocupancy classification is OH-I
- spr type is SU
- the alternative sprinklers are K=79 and K=81 (metric)
- the Hyd Calc is done for K=79,
- piping already installed, just want to use two different types of
sprinklers in the same roof

Apart from this particular case, can there be any generally applicable rule?

Rgds

Aydin