Let me give some more details:

- area is approx. 2500 m2 single space
- the ocupancy classification is OH-I
- spr type is SU
- the alternative sprinklers are K=79 and K=81 (metric)  
- the Hyd Calc is done for K=79, 
- piping already installed, just want to use two different types of
sprinklers in the same roof  

Apart from this particular case, can there be any generally applicable rule?

Rgds

Aydin



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, June 18, 2008 1:10 PM
To: [email protected]
Subject: Re: Sprinkler Mix&Match
Importance: High

Hi Aydin

What is your occupancy? How large is the area? What K-factors you're talking
about?

Cheers
Jack C Kilavuz
Assistant Director
Managing Consultant - RMS
Royal & Sun Alliance Insurance - Singapore
77 Robinson Rd #17-00, Singapore 068896
DID:   (+65) 6423 0552
Fax:    (+65) 6423 0798
Mobile   (+65) 9277 5741
Website: www.rsagroup.com.sg
Note new e-mail address: [EMAIL PROTECTED] Please consider the
environment before printing this e-mail!




Aydın ÖZKAYA <[EMAIL PROTECTED]> Sent by:
[EMAIL PROTECTED]
18/06/2008 04:58 PM
Please respond to
[email protected]


To
<[email protected]>
cc

Subject
Sprinkler Mix&Match






Dear All,

A contractor is in short of sprinklers, while installation. So he wants to
use mix&match; that is, he wants to install two different manufaturer's
sprinklers in the same ceiling; more clearly. 1/3rd of the ceiling will be
from one manufaturer, 2/3rd is from other manufaturer.

Altough the temperature ratings and response type is same, K factors are
slightly different; so they are not identical.

Is this case covered by the code? Is it allowed? What is the article 
number?

Thanks in advance.

Aydin OZKAYA


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


______________________________________________________________
Notice of Confidentiality

This transmission contains information that may be confidential and that may
also be privileged. Unless you are the intended recipient of the message (or
authorised to receive it for the intended recipient) you may not copy,
forward, or otherwise use it, or disclose it or its contents to anyone else.
If you have received this transmission in error please notify us immediately
and delete it from your system.

RSA Group
==============================================================
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to