Because 20 requires the pipe to go to the next size up when the distance is
more than 15 feet, unless proven by calc..


R/

Matt

Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKenzie Rd.
PO Box 877
Cantonment, FL. 32533
850-937-1850 Voice
850-937-1852 Facsimile
[EMAIL PROTECTED]
 

----- >-----Original Message-----
----- >From: [EMAIL PROTECTED] 
----- >[mailto:[EMAIL PROTECTED] On 
----- >Behalf Of Charles Thurston
----- >Sent: Tuesday, June 17, 2008 12:31 PM
----- >To: [email protected]
----- >Subject: Pump test line
----- >
----- >Hello sprinklerforum,
----- >
----- >  I ran into a system installed way before my time and 
----- >do not understand
----- >  something. The Fire pump is all plumbed in 6", The 
----- >Pump Test header has
----- >  three 2 1/2" outlets. There is about 30 feet of pipe 
----- >between the test
----- >  header valve and the test header. The test header is 
----- >located about 12
----- >  feet below the pump outlet.
----- >
----- >  My question is:
----- >  Why would they come off the 6" test header line valve 
----- >step the pipe UP to
----- >  8" pipe for that 30 feet then reduce it back down to 
----- >6" to connect to the
----- >  test header? What am I missing?
----- >
----- >--
----- >Best regards,
----- > Charles Thurston                          
----- >mailto:[EMAIL PROTECTED]
----- >  Coastal Fire Protection
----- >
----- >_______________________________________________
----- >Sprinklerforum mailing list
----- >[email protected]
----- >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
----- >
----- >To Unsubscribe, send an email 
----- >to:[EMAIL PROTECTED]
----- >(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to