Ray,

To answer your questions:

(1) This water purveyor, along with most of the WP's we deal with, require
an RPZ when there is anti-freeze in the system.

(2) The installation of an 1 1/2" RPZ is much more cost efficient than
removing the six inch double check and installing a new 6" RPZ.

(3)  See #2

(4)  The sprinklers with anti-freeze are higher than the interface

(5)  The existing system is about 600 gallons

(6)  The anti-freeze system is about 12 gallons

(7)  See #2

I think you are going towards using the system itself as an expansion
chamber. I personally think that is a great idea, but when you put in an RPZ
as is required here, you need to have the expansion tank. Even if you were
to change out the double check for an RPZ, 13, to the best of my knowledge,
does not make an exception to the expansion chamber requirement based on the
volume of the system you are feeding from.

Thanks,

 Mike Wisneski

 