I already dumped the original post however, as I recall the concern was 
connecting the RPZ to Ferrous or non-ferrous pipe. I assume they have a concern 
for any cathodic reaction between the dissimilar material of the back flow and 
the steel pipe. Could you use a dielectric union between the  RPZ 1-1/2" 
threaded connection and install the expansion tank. 

Mike Cabral

---- Thom McMahon <[EMAIL PROTECTED]> wrote: 
> Mike: 
> 
> A couple of things jump right to mind. 
> 1. What is the purveyors backflow policy? (If they require RPZ protection on
> all Fire Sprinkler systems with anything but water, you'll end up replacing
> your double check with an RPZ.) (If they only require protection for
> non-water additatives, you install an RPZ for the AF heads.)
> 2. Does the Purveyor own the DCBFP? (Most water authorities require
> protection of their water supply, but it is the owners responsibility to
> provide that protection. The owner owns maintains and services the backflow,
> to protect the water system of the purveyor.)(If you install a RPZ for the
> AF heads off the existing Main, you've met all requirements of the Safe
> Drinking Water act 1974, and national primary drinking water regulations.)
> 3. Dose you water authority, have an "Installation Standard" or
> "Installation Guidelines" or "Standard for Backflow Prevention", or a formal
> "Backflow Policy"?
> (I'd read these all very carefully, and if it doesn't match what your being
> told, somebody is making it up as they go, and needs to be stopped.) (Or as
> Geo. Would say "Just Say NO!")
> 
> Thom McMahon, SET
> Firetech, Inc.
> 2560 Copper Ridge Dr
> P.O. Box 882136
> Steamboat Springs, CO 80488
> Tel:  970-879-7952
> Fax: 970-879-7926
> 
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski
> Sent: Wednesday, July 02, 2008 6:21 AM
> To: [email protected]
> Subject: RE: Backflow device and steel pipe
> 
> Well forumites, I've gat a new one (to me).
> 
> Customer wants a small anti-freeze system on a loading dock. The existing
> system is a steel pipe system with a double check backflow at the service
> entry. 
> 
> Normally I would just tap into the closest main (5 feet away), drop down to
> a reduced pressure backflow and install an expansion tank and the eight head
> anti-freeze system.
> 
> The water purveyor now tells me that is unacceptable. They want the
> anti-freeze system tied into the ductile iron pipe at the service entrance,
> before the existing double check, and fed with non ferrous pipe. They say
> they do not want any type of backflow device fed with black steel pipe.
> 
> This, I believe, is not a code issue.
> 
> Has anyone run into this situation before?
> 
> Thanks in advance,
> 
>  Mike Wisneski
> 
>  
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to