Brian,
NFPA 13, 2007 8.8.5.2.1.3 states..."the maximum clear distance required (for
extended coverage UR/Pendent heads) shall be 36-in......"
What needs to be clarified?
This already is clarified from previous editions.
I think it's pretty clear.
36-in. is the MAXIMUM, regardless of the actual 4 times dimension.
Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any use,
disclosure, copying or distribution of this e-mail is unauthorized. If you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, July 14, 2008 2:18 PM
Subject: RE: Sprinkler Pattern Obstructions
Jeff,
That's the confusing part, how can 36" work when the book also says it
needs
to be 96"? I think some clarifying in the next release may be in order.
Brian Harris
FDFP INC.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jeff Hewitt
Sent: Monday, July 14, 2008 2:51 PM
To: [email protected]
Subject: Re: Sprinkler Pattern Obstructions
Brian,
I believe it should be read to mean that the most/furthest away you have
to
be is a maximum of 36-in. The 36-in. is the maximum limit. Without this
provision, you would instead need to be 4 times away or 96-in.
Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer
Bi-State
Fire Protection Corporation
241 Hughes Lane
St. Charles, MO 63301
636-946-0011
636-946-5172 (FAX)
This e-mail and any attachments are CONFIDENTIAL and may be protected by
one
or more legal privileges. It is intended solely for the use of the
addressee identified above. If you are not the intended recipient, any
use,
disclosure, copying or distribution of this e-mail is unauthorized. If
you
received this e-mail in error, please notify the sender immediately at the
above captioned address.
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, July 14, 2008 1:36 PM
Subject: Sprinkler Pattern Obstructions
Forum,
I know I must be reading this wrong but as usual I am in a hurry and
could use some help. NFPA-13 (2007) 8.8.5.2.1.3 states that the
sprinkler shall be positioned a minimum of 4 times the maximum
dimension of the obstruction, but then it goes on to say a maximum of
36" clear space. In my case I have a 24" column I'm trying to avoid
which by the 4 times rule would get me 8'
away, how does the max. 36" clear come into play? Also look at Figure
8.8.5.2.1.3, I'm so confused ........
Regards,
<http://www.firstdefensefire.com/>
E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
5.10250e http://www.pctools.com/en/spyware-doctor-antivirus/
----------------------------------------------------------------------------
----
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/
E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10250e
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]