Marioff (Finland) has developped a pop-out watermist nozzle.
See the video at
http://www.firetechnology.nl/pop-out.html

The nozzle looks rather tamper proof in the standby position, but unfortunately this type of watermist system is sort of a deluge system. Meaning that it requires a separate fire detection system. If a number of cells is connected to one deluge valve, all connected cells will be soaked simultaneously if one detector is activated. Although... the other inmates may "teach" their uncareful colleague not to do that again...

Frans Stoop
TOS architecture & fire protection

At 14:52 14-7-2008 -0500, you wrote:
Problem; we have some institutional sprinklers in a holding cell at a local
jail that repeatedly are getting knocked out by the temporary inmates. Has
anybody come up with a good solution to this problem from our end; specialty
sprinkler guards or anything?

Thank you in advance,

Bobby Gillett

Project Manager

[EMAIL PROTECTED]

(731)-424-0130