I was afraid of that. So it will be 6000 gpm.

Thanks for the help.

Ron

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Wednesday, July 23, 2008 2:17 PM
To: [email protected]
Subject: RE: Fire Flow Calculation

Nope, if you have a building that is not sprinklered in accordance with
NFPA 13 (and you don't because there are unsprinklered areas beyond
those that are allowed to be unsprinklered by NFPA 13) you have an
unsprinklered building.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 5:09 PM
To: [email protected]
Subject: RE: Fire Flow Calculation

It's for fire flow from hydrants. I guess I'm wondering if we can
pro-rate the unsprinklered percentage. If we use 50k sqft with no credit
for sprinklers and 300k sqft at a 75% reduction and add them together or
something to that effect. 

Ron
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Matt
Willis
Sent: Wednesday, July 23, 2008 1:47 PM
To: [email protected]
Subject: RE: Fire Flow Calculation

Tables B and C of the IFC ( I think) list the flows.  An intersting
question arises..., if it is not fully sprinkled... I believe you do not
get the nice reduction?.. Is this what you are looking for ?

R/

Matt 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Wednesday, July 23, 2008 3:36 PM
To: [email protected]
Subject: Fire Flow Calculation

Looking for help to determine required fire flow. New addition to
hospital is 200k sqft. 150k sqft existing building with 50k sqft of the
150k not sprinklered. Construction type is I-FR.

Ron Fletcher
Aero Automatic
Phoenix, AZ
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com 
Version: 8.0.138 / Virus Database: 270.5.5/1569 - Release Date: 7/23/2008
1:31 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to