You could use this as an opportunity to sell putting sprinklers in that 50k Sf if they can't meet the fire flow.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 3:22 PM To: [email protected] Subject: RE: Fire Flow Calculation I was afraid of that. So it will be 6000 gpm. Thanks for the help. Ron -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Paul Pinigis Sent: Wednesday, July 23, 2008 2:17 PM To: [email protected] Subject: RE: Fire Flow Calculation Nope, if you have a building that is not sprinklered in accordance with NFPA 13 (and you don't because there are unsprinklered areas beyond those that are allowed to be unsprinklered by NFPA 13) you have an unsprinklered building. Paul J. Pinigis, P.E. Chief Life Safety Engineer -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 5:09 PM To: [email protected] Subject: RE: Fire Flow Calculation It's for fire flow from hydrants. I guess I'm wondering if we can pro-rate the unsprinklered percentage. If we use 50k sqft with no credit for sprinklers and 300k sqft at a 75% reduction and add them together or something to that effect. Ron -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Matt Willis Sent: Wednesday, July 23, 2008 1:47 PM To: [email protected] Subject: RE: Fire Flow Calculation Tables B and C of the IFC ( I think) list the flows. An intersting question arises..., if it is not fully sprinkled... I believe you do not get the nice reduction?.. Is this what you are looking for ? R/ Matt -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Wednesday, July 23, 2008 3:36 PM To: [email protected] Subject: Fire Flow Calculation Looking for help to determine required fire flow. New addition to hospital is 200k sqft. 150k sqft existing building with 50k sqft of the 150k not sprinklered. Construction type is I-FR. Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - http://www.avg.com Version: 8.0.138 / Virus Database: 270.5.5/1569 - Release Date: 7/23/2008 1:31 PM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)