The presence of a return air plenum doesn't automatically necessitate 
sprinklers.  Sprinklers are going to be required in the space if combustibles 
with ratings equal to or above that which is allowed for a concealed space are 
present as defined in NFPA 13.

If it is a plenum it may actually be beneficial from a fire protection 
standpoint in that the utilities within that plenum have to be specifically 
rated for such use, thus minimizing their risk for fire and smoke spread.  This 
may result in no need for sprinklers in the plenum space.

You could put in 2x2 or 4x4 free return (without ductwork) grilles into the 
ceiling for that matter and it wouldn't change the combustible nature of the 
space above the ceiling.  Also the HVAC units will or should have smoke 
detection to sense any smoke present from the return air.  Unit smoke detection 
 of course will depend on the size of the air handlers.






Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, August 05, 2008 9:59 AM
To: [email protected]
Subject: RE: Floating Ceilings

You can have an unlimited number 2'x4' return air grills in the ceiling without 
adding sprinklers above but put a 4" wide slot around edge of the room and 
sprinklers are required. Go figure.

Where do you get "a plenum thus requiring sprinklers"?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Maag, Barry
Sent: Tuesday, August 05, 2008 6:08 AM
To: [email protected]
Subject: RE: Floating Ceilings

I have seen these types in the past and the "space" around the floating ceiling 
was used for the return air for HVAC. This made the area above the ceiling a 
plenum thus requiring sprinklers


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Rick Green
Sent: Tuesday, August 05, 2008 7:59 AM
To: [email protected]
Subject: Floating Ceilings


I am in the design phase installing wet pipe sprinkler systems protecting new 
schools.

I have noticed that in several of the rooms in the schools(cafeteria, band 
room, main corridor that runs the length of the school), architect has designed 
lay-in ceiling systems with gaps ranging from 4" to 12"
along the walls and between sections of ceiling within the rooms (floating 
ceiling sections).

I do not believe my non-combustible concealed space above the ceilings is 
concealed anymore and may require protection.

Has anyone dealt with this?

I have heard some discussion that if the total square feet of the openings is 
below a certain percent of the total square foot of a space, sprinkler 
protection above the space may not be required?

Interesting thing is that the school is being built as a "Green" project and 
seems like the designed openings would make the schools less energy efficient.

Anyone's help would be most appreciated...



Rick E. Green
District Manager
East Coast Fire Protection, Inc.
1113 Cavalier Boulevard
Chesapeake, Virginia 23323
757/485-7486(p), 757/295-0956(direct), 757/328-0131(cell) [EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to