This is more a vertical opening into an otherwise concealed space. It's worth noting that the TC as accepted effectively 2 rows of sprinklers at such locations instead of the entire space. This will most likely be refined slight at the ROC since it currently is based on a percentage of the dimension of the longest length of the remote area - yea too complicated when such a simple answers exists (ie 2 rows). Sometimes the sprinkler scientists try to make things to academically pure despite the fact that we abandoned that boat loooooong ago.

Roland

On Aug 5, 2008, at 10:17 AM, Fletcher, Ron wrote:

Okay, here is an actual case in design now, I'm not making this up. The
room is 27'x 27' with 2 ft. wide gap between the walls and ceiling on
three sides. Two sides have sheet rock from the ceiling to the deck. The third side has return air grills set on edge vertically for the full 25
ft. dimension creating a 50 sqft continuous return. Do the return air
grills have any effect on the requirement for sprinklers in the plenum?

NFPA does not allow any wiggle room (IMHO) and requires sprinklers
throughout when it is not a concealed space. AHJ's have no incentive to allow anything less than the minimum and potentially a big down side if
they do, so we always add sprinklers above the ceiling.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ