The Tyco tests very conspicuously did not, nor does the listing include doors or moving casement windows. Fixed glass only, no horizontal mullions or bumps. The obvious being that the intent is to cool the glass and maintain separation, not water an opening in hopes of keeping fire and combustion byproduct from breaching it.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Tuesday, September 30, 2008 8:19 AM To: [email protected] Subject: RE: Window Sprinklers Can glass door be protected by a window sprinkler? Ron Fletcher -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton Sent: Tuesday, September 30, 2008 8:00 AM To: [email protected] Subject: RE: Window Sprinklers ??? Actually, the only ways that I'm aware of are to use rated glass - VERY expensive - or window sprinklers. If you don't protect them, there's a limit to the maximum percentage of rated wall area that can be glazed openings, depending on whether it's one or two hours. Otherwise, to make an all-glass wall you would have to use sprinklers or rated glass block or glazing. Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill Sent: Tuesday, September 30, 2008 7:46 AM To: [email protected] Subject: RE: Window Sprinklers Well if it's not mandatory could someone provide the code reference to another solution for a RATED GLASS WALL? We know how to do unrated and know how to do non-glass. Chris -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Tuesday, September 30, 2008 9:27 AM To: [email protected] Subject: RE: Window Sprinklers That's correct, not mandatory but an excellent and tested item. So as long as you can prove that your sprinkler protection of the glazing provides a fire resistant rating equal to that of the wall, you're good to go. Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Russell Sent: Tuesday, September 30, 2008 10:21 AM To: [email protected] Subject: RE: Window Sprinklers "listed" Craig L. Prahl, CET "listed" appears to be the key word here. I just received a phone call from a representative of Tyco and in essence this sprinkler is better technology and is an option and not mandatory. Thank everyone for your response to my post. As usual they are a great help. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3483 (20080930) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 3483 (20080930) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 3483 (20080930) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 3483 (20080930) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)