Timothy: You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in the Light Hazard Areas. There is no "overall building design approach"; the building is not Light Hazard unless ALL areas of the building are light hazard.
I believe the statement in Chapter 11 pertains to new as well as existing structure. You can deduct the hose stream requirements from the tank volume as long as there are no hose stations inside or outside the building that are supplied from the pump and tank. My guess would be that there is not. Mark A. Sornsin, PE Fire Protection Engineer Ulteig Engineers, Inc. Fargo, ND 58104-7079 Direct: 701. 280.8591 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Timothy W Goins Sent: Tuesday, November 18, 2008 9:33 AM To: [email protected] Subject: Existing Pipe Scheduled System Water Supply A water supply analysis (Flowtest) for the proposed installation of a backflow preventer on a pipe scheduled system (Nursing Home) indicates that there is 531 GPM @ 8 PSI at the BOR. It will need a fire pump and storage tank. Please help me with the follwing questions... 1. The nursing home is "Light Hazard" but has "Ordinary Hazard" areas such as the Kitchen and Linen storage areas. I say we need to provide for the "Ordinary Hazard" (Worse Case) but the owner naturally wants the lower demand. What say ye? 2. 11.2.2.7 NFPA 13 2007 says I can use the lower gpm/duration of Table 11.2.2.1 when the system is monitored, but 11.2.2.9 says I can only use the lower values when the building is noncombustible or there is compartmentalization of 3000 ft² (LH) or 4000 ft² (OH). The building is NOT noncombustible construction and does not meet the compartmentalization criteria. Does this statement pertain to existing structures? 3. Since I will have to use a pump and tank, can I deduct the hose streams from the chosen supply requirements of Table 11.2.2.1? Timothy W Goins A & T Services "For I am not ashamed of the gospel of Christ: for it is the power of God unto salvation to everyone that believeth;..." KJV Romans 1:16 Reply to <mailto:[EMAIL PROTECTED]> mailto:[EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)