Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in the 
Light Hazard Areas.  There is no "overall building design approach"; the 
building is not Light Hazard unless ALL areas of the building are light hazard.

I believe the statement in Chapter 11 pertains to new as well as existing 
structure.

You can deduct the hose stream requirements from the tank volume as long as 
there are no hose stations inside or outside the building that are supplied 
from the pump and tank. My guess would be that there is not.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND 58104-7079
Direct:    701. 280.8591

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Timothy W Goins
Sent: Tuesday, November 18, 2008 9:33 AM
To: [email protected]
Subject: Existing Pipe Scheduled System Water Supply

A water supply analysis (Flowtest) for the proposed installation of a
backflow preventer on a pipe scheduled system (Nursing Home) indicates that
there is 531 GPM @ 8 PSI at the BOR. It will need a fire pump and storage
tank. Please help me with the follwing questions...

1.  The nursing home is "Light Hazard" but has "Ordinary Hazard" areas such
as the Kitchen and Linen storage areas. I say we need to provide for the
"Ordinary Hazard" (Worse Case) but the owner naturally wants the lower
demand. What say ye?

2.  11.2.2.7 NFPA 13 2007 says I can use the lower gpm/duration of Table
11.2.2.1 when the system is monitored, but 11.2.2.9 says I can only use the
lower values when the building is noncombustible or there is
compartmentalization of 3000 ft² (LH) or 4000 ft² (OH). The building is NOT
noncombustible construction and does not meet the compartmentalization
criteria. Does this statement pertain to existing structures?

3.  Since I will have to use a pump and tank, can I deduct the hose streams
from the chosen supply requirements of Table 11.2.2.1?


Timothy W Goins
A & T Services

"For I am not ashamed of the gospel of Christ: for it is the power of God
unto salvation to everyone that believeth;..." KJV Romans 1:16

Reply to   <mailto:[EMAIL PROTECTED]> mailto:[EMAIL PROTECTED]


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to