Out of curiosity where do come up with electrical/mechanical rooms being
OH?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

We need to be careful in our use of words here. This building is a light
hazard occupancy. 

All light hazard occupancy buildings will contain some areas of Ordinary
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the
entire
building, or the hose stream requirements. 

While these areas must be protected per their specific hazard for
density,
if your largest OH II area is only 600 Sf then you only provide OH II
density for that 600 SF area, and any smaller areas of the same hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per
head
with 5.6K will give you 0.20 at just about 7 PSI. So for your 600 Sf you
would calc 8 heads unless your Light hazard area required more than 8
heads,
or was more remote, with the same number of heads.

Now because this was installed pipe schedule, you need to know if OH
pipe
schedule was used in the OH areas? Actually you need to Hydraulic the
entire
system to ensure the loss from the backflow will allow it to work per
NFPA
13, 2007 8.17.4.6.2.  But as far as your question goes "The Occupancy is
Light Hazard" for the use of 11.2.2.1 so 15 Psi and the 30-60 Min.
duration
is OK.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light
in
the Light Hazard Areas.  There is no "overall building design approach";
the
building is not Light Hazard unless ALL areas of the building are light
hazard.

Mark A. Sornsin, PE

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to