There sure are a lot of undersized pressure tanks feeding nursing homes we
did in the late 70's, early 80's if one >400 sf room requires a 1-hour
supply at the higher density.

Back then, especially in the 70's, we scheduled systems and sized the tank
for the spkr supply, going to the min since we'd have central station and
compartmentalization.

glc 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Tuesday, November 18, 2008 3:11 PM
To: [email protected]
Subject: RE: Building Classification (change from pipe schedule water
supply)

Very good post, Chris.

Section 11.1.5.2 (3) of the '07 helps address this issue.

Ed Kramer
Littleton, CO


> Now you do have a point on what to do with an all light hazards but
> there is
> 1 - 3' x 2' reach in closet.  I don't have a good handle on when a
> single
> head OH changes to a full OH design other than 14.4.4.4.2 allowing the
> omission from calcs for closets.  So if it's a 2 head closet do you have
> an
> OH calc?