You seem to contradict what Mark said. I have to go with Mark, there is no
such thing as a building classification in 13. We look at each area or room
and apply the right protection scheme including hose for that room or area.
If all are light hazard and you have a legitimate 600 sq.ft. kitchen you
will have at least one calc. with 250 gpm hose added. And unless you are
using the room design you still need to go to a full 1500 sq.ft. (modified
as necessary) designed part OH part LH with 250 hose.
What do you do with a 100,000 sq.ft. OH factory and say 2,000 sq.ft. of HPS?
I would think 500 gpm hoses on at least one calc and 250 throughout the
OH's.
Now you do have a point on what to do with an all light hazards but there is
1 - 3' x 2' reach in closet. I don't have a good handle on when a single
head OH changes to a full OH design other than 14.4.4.4.2 allowing the
omission from calcs for closets. So if it's a 2 head closet do you have an
OH calc?
When in the building code we lean more toward building classifications but
even that is not fully accurate. For example a school as a building will be
an E, but it will have at least A (gym), B (office) and F (kitchen). These
do get looked at individually for size and separations and treated
individually for most aspects.
So we do need to be careful with the words and not classify building but
hazards.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [EMAIL PROTECTED]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 12:15 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply
We need to be careful in our use of words here. This building is a light
hazard occupancy.
All light hazard occupancy buildings will contain some areas of Ordinary
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the entire
building, or the hose stream requirements.
SNIP
Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Timothy:
You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in
the Light Hazard Areas. There is no "overall building design approach"; the
building is not Light Hazard unless ALL areas of the building are light
hazard.
Mark A. Sornsin, PE
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)