Ron,

The IBC doesn't reference NFPA 15 and the IFC references NFPA 15 
references is very limited. Unless a jurisdiction specifically adopts NFPA 
15, there is no legal requirement to follow it.

In the project I cited, in order to save the owner several hundred 
thousand clams, I had recommended protecting only the front and tail ends 
of the limestone conveyor.  The belt was fire resistive and conveyor was 
also interlocked to shut down upon actuation of the lineal heat detection 
cable.  The project was a flue gas desulfurization project for an 
industrial power plant. There was no insurance requirement to protect the 
entire conveyor.

Also, I was involved with two(2) other coal fired power plants with 
similar limestone conveyors and neither was required by FM to be provided 
with water spray protection.

That being said, based on Stewart's story of an explosion and fire at a 
British Steel plant that exposed a limestone conveyor, I am not as staunch 
in my opinion.

Regards,

James L.(Jim) Roberts, PE
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Rod DiBona" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
11/25/2008 01:23 AM
Please respond to sprinklerforum

To
<sprinklerforum@firesprinkler.org>
cc

Subject
RE: Coal conveying belts FM standards







Thanks for the reply Jim. Actually I am referring to the gallery that the 
conveyor belt is enclosed in. It is a tubular gallery (therefore 
enclosed). There will be an interlock to shut down the conveyor. When you 
say that protection of the top and return belt is "overkill" in your 
opinion, which is what I am hearing from others; how do you reconcile the 
NFPA 15 standard that says to protect the "top and bottom belt surface 
area...?" I feel like this is clearly spelled out in the standard yet I 
see that FM doesn't seem to require it so I am scratching my head on this 
one. 
 
Thanks for the help.
 
Rod DiBona
Rapid Fire

________________________________

From: [EMAIL PROTECTED] on behalf of 
[EMAIL PROTECTED]
Sent: Mon 11/24/2008 7:17 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Coal conveying belts



Ron,

When you say "tube style", I am assuming that is the same as "pipe"
conveyors where the belt is open at loading and unloading ends, but is
"wrapped" closed by idlers for travel between conveyor ends and is flat
for the return travel.  Is that correct?

If the belt is fire resistive, it might not need water spray protection
for the return belt depending upon the quantity of coal dust still
adhering to the belt.

I have recently done a 1000 ft. limestone conveyor of this type, where the
client wanted both belts protected even though the belt was fire resistive
and belt motors were interlocked to shut down the conveyor. - over kill in
my opinion, since limestone is inert.

For that situation, spray nozzles were provided over the top of the top
conveyor and at the side to spray between belts and below the return belt.

Regards,

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





"Rod DiBona" <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
11/21/2008 06:33 PM
Please respond to sprinklerforum

To
<sprinklerforum@firesprinkler.org>
cc

Subject
Coal conveying belts







I am wondering what is typically done when covering an elevated (40' and
higher) and enclosed tube style coal conveyor. The property in question
is an FM property. The dilemma that I am trying to resolve is that when
looking at FM data sheets 7-11 and 4-1N it only shows and talks about
configurations to cover the top belt with no mention whatsoever of the
return belt. NFPA #15 7.2.3.3.2 says "Discharge patterns of water spray
nozzles shall envelop at a net rate of not less than .25 gpm/ft, the top
and bottom belt surface area, conveyor surfaces where combustible
materials are likely to accumulate, the structural parts, and the idler
rolls supporting the belt."



This seems to be a rare case where FM's requirement is less stringent
than NFPA. In this case I am dealing with Powder River Basin coal which
is more likely to spontaneously combust than coal from other areas so I
would really feel better about doing both belts. At the end of the day
FM will dictate the minimum but I wanted to be fully informed to give
the owner all options. Thanks for your input as always.



Rod DiBona

Rapid Fire

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person
or entity to which it is addressed and may contain
proprietary, business-confidential and/or privileged material. 
If you are not the intended recipient of this message you are
hereby notified that any use, review, retransmission, dissemination,
distribution, reproduction or any action taken in reliance upon
this message is prohibited. If you received this in error, please
contact the sender and delete the material from any computer. 

Any views expressed in this message are those of the individual
sender and may not necessarily reflect the views of the company. 
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to