In my opinion, the NFPA 13 hose stream demand must be added in order to
comply with 903.3.5.2.  The writers of this section intentionally added
hose stream demand to Section 903 in order to distinguish a high-rise
building water supply from the typical tank-fed sprinkler system where
no hose stream demand is accommodated (NFPA 13 11.1.5.1, 12.8.1).  The
standpipes, and the NFPA 14 references, are located in Section 905 where
there is no corresponding high-rise supplementary water supply.  I think
this is the answer if you are the IBC AHJ.  If the IFC AHJ wants 250 gpm
hose streams when a seismic event disrupts the public water supply, then
your local code should be amended to state this.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: Hi Rise Secondary Source ... again
From: Dave <[email protected]>
Date: Thu, December 11, 2008 1:35 pm
To: [email protected]

Greetings all..

I know I brought up this general topic once before but bear with me on
it again.  IBC-2006 Section 903.3.5.2 is the requirement for secondary
on-site water supply in high rise buildings.  Presuming we have an
eligible building it comes down to sizing the storage tank or vessel.

Code says 30 minutes of sprinkler demand - no problem on that part.  It
gets muddy at 'including hose stream allowance' -- here's my dilemma.

This is a high rise building and it also requires a standpipe to NFPA
14.  Many times this means a combination riser for sprinkler and
standpipe.  Now NFPA 14 tells us that when designing such combinations
we do not apply the hose stream allowances of NFPA 13 since 14 is the
hose stream standard when it comes to a standpipe system - still with me
??

How do I use a hose stream allowance for tank sizing when Im told not to
apply hose stream allowances in the overall design and in reality the FD
will be hooking up 2 1/2" hoses to the hose valves and pulling +200 GPM
for hoselines.  Do we calculate the 250 GPM as the 'hose stream
allowance'?  If we use the 100 GPM hose stream in NFPA 13 in spite of
all this then we will be flowing +200 and having only designed for 100
GPM we will no longer have the 30 minutes of sprinkler duration in a
common riser system.

What say everyone else - I'm totally up in the air and need something to
go with.

Dave P.
AHJ in NJ
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to