Just as a plumber would assume testing a sprinkler backflow is limited to
the backflow portion of the test, not aware of the forward flush we're more
concerned about.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Friday, February 27, 2009 9:56 AM
To: [email protected]
Subject: Re: Fire marshall

In Washington a fire sprinkler contractor can put in the backflow for
the sprinkler if it's outside the building perimeter. If inside it has
to be a plumber. My favorite part is that the sprinkie can put in the
UG to the flange and the piping after the backflow but the plumber has
to be called in for the backflow and any transition pieces of potable
pipe that may be required between the entry flange and the backflow
device. The rationale is always explained to be due to technical
expertise of the various trades but this is obviously political issue
of authority related to possession of a piece of work. You can ask the
head of the state board of plumbers if he thinks that sprinkler guys
are unqualified to put in this item face to face and he'll answer yes.
I don't think he's that stupid. I do think he understands politics.

On Fri, Feb 27, 2009 at 4:50 AM, Craig Leadbetter
<[email protected]> wrote:
> We have a local area that will not allow fire sprinkler contractors to
> test,
> service or install backflows on fire sprinkler systems (even on the
> anti-freeze loops).
>
>
> This is the way it is in the entire state of Michigan. Sprinkler
> contractor cannot even help the plumber install the backflow.
>
> Craig Leadbetter
> Safeguard of Marquette
> (P)906-475-9955 Ext 101
> (F) 906-475-5474
> (C) 906-362-5393
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Thursday, February 26, 2009 8:09 PM
> To: [email protected]
> Subject: Re: Fire marshall
>
> The State Marshal may not have the statutory power to do anything.
> In Ohio, they cannot override the local AHJ. In fact, the local AHJ
> could
> tell the State Fire Marshal to.....well, you get the idea.
> We have a local area that will not allow fire sprinkler contractors to
> test,
> service or install backflows on fire sprinkler systems (even on the
> anti-freeze loops). A plumber must be used!
> We have another AHJ that told me we must have a licensed fire alarm
> company
> on-site to push the alarm silence button when we do the annual
> inspection!
> When I called the State, he told me their office has no power except in
>
> motels and state buildings.
> Of course, the law is the law and a court can force anyone to adhere to
> it.
>
>
> Forest  Wilson
>
> Project Manager
> Cherokee Fire Protection Co.
> 3195  Dayton Xenia Rd Ste 900
> Dayton OH 45434
>
> ph: 937-376-2333
> fx:  614-455-4324
> cell: 937-307-5647
>
> Visit our blog: _www.cherokee-fire.blogspot.com_
> (http://www.cherokee-fire.blogspot.com/)
>
>
> FIRE SPRINKLERS SAVE LIVES!!
>
>
>
> NOTICE: The information contained in this  email is intended to be
> solely for
> the use of the named individual or entity to  which it is directed and
> may
> contain information that is privileged or otherwise  confidential. It is
> not
> intended for transmission to, or receipt by, anyone  other than the
> named
> addressee (or a person authorized to deliver it to the  named
> addressee). It should
> not be copied or forwarded to any unauthorized  persons. If you have
> received
> this electronic mail transmission in error, please  delete it from your
> system
> without copying or forwarding it, and notify the  sender of the error by
> reply
> email or by calling Cherokee Fire Protection Co. at  888-347-3079 toll
> free.
>
>
> In a message dated 2/26/2009 8:02:50 P.M. Eastern Standard Time,
> [email protected] writes:
>
> Roland  you are 100% correct.  The problem we are having is that when a
> local
> AHJ  (who has minimal knowledge of any code gets confused they say that
> they
> have  no one to discuss it with at a higher level so they guess.  I have
> even
> had a discussion with one (where i showed him in 13 where the book said
>
> differently from what he thought it said) where he said "too bad for you
> im  the
> highest level there is do it my way."  When a fellow tech called an  AHJ
> and
> informed him of a customers system the AHJ said i dont care about that
> stuff.
>
>
>
>
> ________________________________
> From:  Roland Huggins <[email protected]>
> To:  [email protected]
> Sent: Thursday, February 26, 2009 9:08:19  AM
> Subject: Re: Fire marshall
>
> Also worth noting that just because a  state fire marshal exists does
> not
> mean that they resolve differences in  interpretation between local
> AHJ's or act
> as a higher authority over-ruling a  local AHJ's interpretation.
>
> Roland
>
>
>>
>>
>>
>> _______________________________________________
>>  Sprinklerforum mailing list
>>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For  Technical Assistance, send an email to:
> [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]
>> (Put the word unsubscribe  in the subject field)
>>
>>
>>  _______________________________________________
>> Sprinklerforum mailing  list
>>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> For  Technical Assistance, send an email to:
> [email protected]
>>
>> To Unsubscribe, send an email
> to:[email protected]
>> (Put the word unsubscribe  in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum  mailing  list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For  Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in  the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing  list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For  Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in  the subject field)
>
> **************A Good Credit Score is 700 or Above. See yours in just 2
> easy
> steps!
> (http://pr.atwola.com/promoclk/100126575x1218822736x1201267884/aol?redir
> =http:%2F%2Fwww.freecreditreport.com%2Fpm%2Fdefault.aspx%3Fsc%3D668072%2
> 6hmpgID
> %3D62%26bcd%3DfebemailfooterNO62)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to