I am currently working on a project where we ran into a similar problem (I think I mentioned it in earlier posts) The problem there was that the water supply varies almost 30 psi at any given time of the day. There were three water towers on the system that would fill at random times (it has changed, but not sure how at this point). The water company had no ideal until they put a pressure recorder on a hydrant for about 5 days. This town does their own water tests and they provide the data.

This type of thing is almost impossible to track. What are you going to to, put a recorder on the pump for 3 days, find out when the lowest pressure is and then schedule the test? Nice in theory, but it is tough to get most contractors to do water tests anyway (from an independent designer perspective) without adding that extra dimension.

The interesting thing with this job is that we are going to have to add a fire pump and now we have to size it based on the maximum pressure, not necessarily what we agreed on for the "typical" pressure (the max was 92 psi and everybody agreed on 72 as the pressure was above that 95% of the time)


At 09:31 AM 2/27/2009, you wrote:
Question for the lettered members and others with experience and/or an opinion -

I recently looked at the riser of a new system installed in my home town. The system requirement according to the hyd. calc. nameplate states 377.9...@75psi. The system gauges read 60psi static. When I contacted the water superintendent he stated the installing contractor took the hydrant flow information used to design the system. He also stated that he head been asked to have the standpipe full and to have both Town pumps turned on before the hydrant was flowed. He continuede that it is standard procedure to have a water department employee respond to the water plant for every fire department discharge to turn on the pumps. He stated the standpipe is filled once weekly prior to weekends so that water employees do not have to work weekends then the standpipe is drawn down, filled during the week..... It appears the "best case scenario" was used in taking the hydrant flow making the system suffient only when the standpipe is filled and both pumps are in operation. I do not see anything in 13 which tells anyone how to determine the acceptability of hydrant flow data, however if the gauge states there is 15 pounds less static pressure than what is required residually for the system to operate - then there is a problem. Is there any requirement for engineers or others to apply acceptability standards to hydrant flow data or can the results purposely be slanted? It seems the system will operate properly Thursday 10am through Friday at 4pm....... The local AHJ states he accepted the opinion and acceptance of the engineer hired to review and accept the system. I do not know if this firm or individual has any training in fire protection systems, or if he has provided any such credentials to the AJH. This is in the State of NY.

opinions? thoughts? code references? standard references?

thanks in advance,
Garth
retired fitter

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to