It is true that the laboratory test standards do not fit into the hierarchy of 
code enforcement;; however, NFPA 13 requires the products used in sprinkler 
systems to be listed.  As Mike stated, UL 864 requires that  abort switches 
shall not be used on deluge or preaction systems.  If an abort function is 
provided and is used on such systems, it would not meet the functional 
requirements of the test standard and not be recognized as listed.  

Salvatore Izzo, P.E.
Manager - Reliable Technical Services


________________________________________
From: sprinklerforum-boun...@firesprinkler.org 
[sprinklerforum-boun...@firesprinkler.org] On Behalf Of John Drucker 
[john.druc...@verizon.net]
Sent: Tuesday, April 07, 2009 6:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Great question.  Listings don't seem to have the effect one would assume. We
often hear "must be installed in accordance with the listing", or "product
listed for the intended purpose".

Then we see prescriptive code applications such as deck and balcony
sprinklers and smoke alarms used in other then dwelling units. The
government can pretty much do as it pleases in the pursuit of "safeguarding
building occupants and emergency responders"

It's about the hierarchy of code enforcement, it goes something like this;

1. Statutes = The Legislative action, in NJ the "Uniform Construction Code
Act"
2. Regulations = The Department or Commissioner rule making, in NJ the
"Uniform Construction Code"
3. Codes= The where and when side of the equation, in NJ the 2006 IBC/NJ
Edition, amongst many others.
4. Reference Standards = The how side of the equation, in NJ the 2002
Edition of NFPA-13 for example.
5. Manufacturer's Instructions = The specific how for a specific product.
6. Listings = The nationally recognized testing lab that evaluated the
product for fitness.

I'm sure there are variants at municipal, county and even federal levels.

Bottom line if a statute, regulation or code prescribes it then so it shall
be.

Hope that helps,

John Drucker


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jay Jay
Blocker
Sent: Monday, April 06, 2009 11:37 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But where does the UL rank in order?  By this I mean if the local area has
adopted 13 and 25 do they also have to take into account ULs rules or just
say as long as the device is listed it is good?




________________________________
From: Mike Henke <mi...@pottersignal.com>
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why?
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)




_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to