It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: chr...@sentryfiremn.com

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to