Maybe so but UL is not recognized or an adopted Code Set by any government 
entity so while it's wording may be logical and appropriate it's not 
necessarily enforceable.

But in this case I would still cite it and use it to inform Mr. PE that he's 
totally clueless as to what he has designed and specified.

First a D.I.P.A. for a few computers is gross overkill.  Second with supervised 
piping, area smoke detection and closed sprinkler heads, if someone doesn't 
respond to the first alarm or second then it needs to go off.  There is 
absolutely no good reason to have an abort switch in a P.A. system.

But you would be surprised on how many times I've been asked this very 
question.  Once I've explained the sequence of operation of a P.A. system the 
question will go away.

This sounds like one of those projects that would be a real nightmare since 
you're obviously dealing with an EOR who already has his mind made up on what 
is proper and required and probably won't back down and look foolish to the 
owner.  

If you decide to pass I'd write a nice letter to the owner and explain why you 
did not bid on this project.

If you do bid and win, I'd write another letter explaining the proper operation 
and purpose of a D.I.P.A. system and copy the engineer.  Obviously the owner 
and EOR need some additional educating.


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Forest Wilson
Sent: Monday, April 06, 2009 11:50 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: Pre-action abort

But UL is the entity doing the listing. 
Forest Wilson 

-----Original Message-----
From: Jay Jay Blocker <fire_sprinkler...@yahoo.com>

Date: Mon, 6 Apr 2009 20:36:49
To: <sprinklerforum@firesprinkler.org>
Subject: Re: Pre-action abort


But where does the UL rank in order?  By this I mean if the local area has 
adopted 13 and 25 do they also have to take into account ULs rules or just say 
as long as the device is listed it is good?




________________________________
From: Mike Henke <mi...@pottersignal.com>
To: sprinklerforum@firesprinkler.org
Sent: Monday, April 6, 2009 4:45:14 PM
Subject: RE: Pre-action abort

It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.

Regards,

mike

Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, April 06, 2009 4:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Pre-action abort

Question one: Why? 
Question two: At what stage of system response do you want to abort?

There is no mention anywhere in NFPA 13 about the allowance or
disallowance of an abort switch.  I just can't see where anyone would be
quick enough to get to it if something in the system started an
operation anyway.  

With all the delays already built in to a double interlock system what
in the world could another interruption accomplish?

I would not be in favor of it.  But for the sake of curiosity, what's
the application and reasoning behind the question?

Craig L. Prahl, CET  
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com 


-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Chris
Cahill
Sent: Monday, April 06, 2009 5:15 PM
To: sprinklerforum@firesprinkler.org
Subject: Pre-action abort

Can one have an abort button on a double interlock pre-action
(electric/pneumatic)?  I'm assuming it would be like on a clean agent
system.  PE hasn't got back to us (don't really expect him to, not a
surprise).  



Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.



763-658-4483

763-658-4921 fax



Email: chr...@sentryfiremn.com



Mail: P.O. Box 69

        Waverly, MN 55390



Location: 4439 Hwy 12 SW

              Waverly, MN 55390



_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
techsupp...@firesprinkler.org

To Unsubscribe, send an email
to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: techsupp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to