Agreed Ron & Craig  

Craig, when the Architect asked him for his code reference
that required sprinklers, this is the paragraph he referred
to, even though it doesn't have anything to do with the
issue.

  NFPA 13 (1999) 7-1.2
  For buildings with two or more adjacent occupancies that
are not physically separated by a barrier or partition
capable        of delaying heat from a fire in one area from
fusing sprinklers in the adjacent area, the required
sprinkler protection for   the more demanding occupancy
shall extend 15 ft (4.6 m) beyond its perimeter.

We can't seem to find a central management board or
committee.  That is the whole issue.  I think his department
is flawed in this respect but for now my opinions don't get
the builders building opened.  I think the Architect will
pursue the overall issue with standardization soon prior to
any more projects.

I wish all of our legal advice were this reasonable !

Thanks for all the responses.

Don



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf
Of Ron Greenman
Sent: Friday, May 01, 2009 10:06 AM
To: [email protected]
Subject: Re: Detached Porte Cochere

We're all running on presumptions here, including,
apparently, the
AHJ, but if the construction type, size and occupancy of the
porteco
do not require sprinklers by any state or local code and if
the
separation is sufficient to not present an exposure (you'll
have to do
your own code checking, or better yet the architect needs
to) then
sprinklers are not required. NFPA 13 will not tell you in
any place
what types of structures, based on occupancy, size,
construction type
or exposure, need sprinklers but it will tell you where and
how to lay
out sprinklers when necessary. THIS IS NOT A SPRINKLER
ISSUE! At least
not yet. And again, in countries subscribing to a western
liberal
democratic philosophy (disclaimer; Republicanism is western
liberal
democratic before I start a political debate--not capital R,
lower
case d), particularly one based on English Common Law, you
are free to
do whatever you want provided you harm no one else and any
proscription to that basic concept must be in writing and
specific.
You can't do it because a proscriptive document (NFPA 13 for
instance)
doesn't mention that you can does not hold water. Once
again, very
cheap legal advice.

On Fri, May 1, 2009 at 7:40 AM,  <[email protected]>
wrote:
> So where is his documentation saying that sprinklers are
required?  Remember we've discussed this kind of situation
many times.  So before caving in I'd ask for the code
references upon which he bases his opinion.  I'd tell him
that the owner isn't going to provide something unless it's
required and the owner needs to see it in writing in the
"code".
>
> Tell him you're going to have to get a change order from
the owner and you need proof of the requirement.  That way
it's not a direct challenge and forces him to come up with
black and white requirements not just "sumthin he thunk up".
 If he can't produce it then throw it back at him.
>
> Other measure is to call his department manager or other
supervisor for a clarification, don't give names or
projects, you're just doing research of a requirement for a
prospective project and get them to provide chapter and
verse if it is a requirement of theirs.  Then make sure to
get a name, log the time and date and take good notes.  If
you can get them to e-mail you the same info that would be
even better.  If it turns out to not be a requirement you
can use the name and date and quote the response to the
local yokel.
>
>
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf
Of Don Lowry
> Sent: Friday, May 01, 2009 10:13 AM
> To: [email protected]
> Subject: RE: Detached Porte Cochere
>
> Rick,
>
> Yes, that is the issue.  The builder / Architect don't
want to do the required connection of the buildings, but the
DADS Inspector for this region apparently interprets
differently than the last regional inspector did.
 Unfortunately there doesn't seem to be a standard
statewide, and the decisions are left to the individual
inspectors.  This makes it hard for the builders to have a
set of specific rules to follow when designing the building.
Since the DADS inspectors don't review drawings prior to
construction, (Arch or FP) it ends up being an issue when
it's down to the wire to open. This particular inspector
made the statement that he "didn't care what the IBC or IFC
states, we use NFPA codes" and it didn't matter if the
city's Building Official or Fire Marshal said.
> Guess this will be a learning experience for the
Architect.
>
> Thanks for the responses.  I can tell the builder that I
tried :>)
>
> Don
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On
Behalf Of Matsuda, Richard
> Sent: Friday, May 01, 2009 8:15 AM
> To: [email protected]
> Subject: RE: Detached Porte Cochere
>
> Don,
> If this is some kind of care facility in Texas, then the
state inspector has slightly different requirements...and if
you don't comply, then the care facility might not receive
state certification or any state funding.
> The state inspector might be interpreting the 6-foot
clearance between the buildings as insufficient for this
combustible construction...and so he considers the porteco
as part of the main building.
>
> rick matsuda
> city of dallas
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On
Behalf Of Don Lowry
> Sent: Friday, May 01, 2009 6:32 AM
> To: sprinklerfo...@firesprinkler. org
> Subject: Re: Detached Porte Cochere
>
> Combustible
> Don Lowry
> Sent via BlackBerry
> _______________________________________________
> Sprinklerforum mailing list
>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
> um
> For Technical Assistance, send an email to:
> [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
um
> For Technical Assistance, send an email to:
[email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
>
http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
um
> For Technical Assistance, send an email to:
[email protected]
>
> To Unsubscribe, send an email
to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
um
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to