So where is his documentation saying that sprinklers are required?  Remember 
we've discussed this kind of situation many times.  So before caving in I'd ask 
for the code references upon which he bases his opinion.  I'd tell him that the 
owner isn't going to provide something unless it's required and the owner needs 
to see it in writing in the "code".

Tell him you're going to have to get a change order from the owner and you need 
proof of the requirement.  That way it's not a direct challenge and forces him 
to come up with black and white requirements not just "sumthin he thunk up".  
If he can't produce it then throw it back at him.  

Other measure is to call his department manager or other supervisor for a 
clarification, don't give names or projects, you're just doing research of a 
requirement for a prospective project and get them to provide chapter and verse 
if it is a requirement of theirs.  Then make sure to get a name, log the time 
and date and take good notes.  If you can get them to e-mail you the same info 
that would be even better.  If it turns out to not be a requirement you can use 
the name and date and quote the response to the local yokel.

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Don Lowry
Sent: Friday, May 01, 2009 10:13 AM
To: [email protected]
Subject: RE: Detached Porte Cochere

Rick, 

Yes, that is the issue.  The builder / Architect don't want to do the required 
connection of the buildings, but the DADS Inspector for this region apparently 
interprets differently than the last regional inspector did.  Unfortunately 
there doesn't seem to be a standard statewide, and the decisions are left to 
the individual inspectors.  This makes it hard for the builders to have a set 
of specific rules to follow when designing the building. Since the DADS 
inspectors don't review drawings prior to construction, (Arch or FP) it ends up 
being an issue when it's down to the wire to open. This particular inspector 
made the statement that he "didn't care what the IBC or IFC states, we use NFPA 
codes" and it didn't matter if the city's Building Official or Fire Marshal 
said.
Guess this will be a learning experience for the Architect.

Thanks for the responses.  I can tell the builder that I tried :>)

Don

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matsuda, Richard
Sent: Friday, May 01, 2009 8:15 AM
To: [email protected]
Subject: RE: Detached Porte Cochere

Don,
If this is some kind of care facility in Texas, then the state inspector has 
slightly different requirements...and if you don't comply, then the care 
facility might not receive state certification or any state funding.
The state inspector might be interpreting the 6-foot clearance between the 
buildings as insufficient for this combustible construction...and so he 
considers the porteco as part of the main building. 

rick matsuda
city of dallas 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Don Lowry
Sent: Friday, May 01, 2009 6:32 AM
To: sprinklerfo...@firesprinkler. org
Subject: Re: Detached Porte Cochere

Combustible
Don Lowry
Sent via BlackBerry
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerfor
um
For Technical Assistance, send an email to:
[email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to