Adam, Realize that the "re-galvanizing" will be "cold" spray-on galvanic paint. You may wish to discuss this with your client. You can get galvanized couplings and I believe galvanized mech tees with factory applied zinc. Also, even with precautions the fabricators are put at a greater risk when welding on galvanized pipe. talk to your Victaulic rep about solutions before making a final decision.
On Tue, May 12, 2009 at 7:20 AM, Davis, Adam <[email protected]> wrote: > > The client has agreed to use grooved connection for the 6" main but not for > the 2". It seems the practical solution is to use TOLs and re-galvanize to > save on field labor and cost. I'm unfamiliar with galvanized pipe so the > forum's input has been helpful. Thanks > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of > [email protected] > Sent: Tuesday, May 12, 2009 10:09 AM > To: [email protected] > Subject: RE: Galvanized pipe - threaded reducer tees vs. thread-o-lets > > Is there a requirement to use threaded versus grooved? > > If you have corrosion issues the "clamp fittings" aren't galvanized so they > could corrode so it's logical that you'd avoid them. > > If you are threading pipe, the field install labor would be less if you have > the thread-o-let in the main. From a materials cost the TOL would also come > out cheaper, from all areas of installation the TOL would be cheaper. Sure > the shop labor would be more for the TOL but that would have to be greatly > offset by the other savings in labor and materials. > > Also I hope you don't intend to ask for 6" threaded pipe, 2" will get enough > frowns. > > > > > Craig L. Prahl > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Davis, Adam > Sent: Tuesday, May 12, 2009 9:29 AM > To: [email protected] > Subject: Galvanized pipe - threaded reducer tees vs. thread-o-lets > > I have a 6" galvanized main and have to come off with 40 2" branch lines. > I'm trying to determine the least costly way to transition to the 2" branch > lines. The two options I have are using 6"x2" threaded reducer tee or 2" > thread-o-let and re-galvanizing the weld. The client requires galvanized > pipe and does not want to use mechanical clamp fittings. Any suggestions to > which method is the least expensive? > > > > Thanks > > Adam Davis > > > NOTICE - This communication may contain confidential and privileged > information that is for the sole use of the intended recipient. Any viewing, > copying or distribution of, or reliance on this message by unintended > recipients is strictly prohibited. If you have received this message in > error, please notify us immediately by replying to the message and deleting > it from your computer. > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > NOTICE - This communication may contain confidential and privileged > information that is for the sole use of the intended recipient. Any viewing, > copying or distribution of, or reliance on this message by unintended > recipients is strictly prohibited. If you have received this message in > error, please notify us immediately by replying to the message and deleting > it from your computer. > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)