What's the client's basis for not allowing "mechanical clamp fittings"? By far the best way to do this would be to cut saddles in the field. By far - no galvanized welding issues, no threading ... way too easy.
Steve Leyton Protection Design & Consulting San Diego, CA -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Davis, Adam Sent: Tuesday, May 12, 2009 6:29 AM To: [email protected] Subject: Galvanized pipe - threaded reducer tees vs. thread-o-lets I have a 6" galvanized main and have to come off with 40 2" branch lines. I'm trying to determine the least costly way to transition to the 2" branch lines. The two options I have are using 6"x2" threaded reducer tee or 2" thread-o-let and re-galvanizing the weld. The client requires galvanized pipe and does not want to use mechanical clamp fittings. Any suggestions to which method is the least expensive? Thanks Adam Davis NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) __________ Information from ESET NOD32 Antivirus, version of virus signature database 4067 (20090512) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com __________ Information from ESET NOD32 Antivirus, version of virus signature database 4068 (20090512) __________ The message was checked by ESET NOD32 Antivirus. http://www.eset.com _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)