Our typical (Non-Seismic) installation above a ceiling is 8-1/2" to center
of pipe. This allows us to use a 6" nipple and reducer to recessed heads.
This normally requires a 1'-0" Min. space below duct work for elect, lights,
sprinkler and support hangers for the duct work, since BOD will require an
additional 1" to 3" for supports depending on size of duct

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Friday, July 31, 2009 10:36 AM
To: [email protected]
Subject: Re: Renegade HVAC Contractor

Garth,

Are you in a seismic zone? I've found high to be better when you have a lot
of bracing but I'd otherwise agree with your comments.

On Fri, Jul 31, 2009 at 9:29 AM, Garth W. Warren<[email protected]>
wrote:
> Everyone on here seems to be suggesting hanging high.  From a 
> different perspective I always requested a 6" or 8" clear space 
> directly above the space required by the electrician for light and 
> their installation (usually
> 6 to 8").  