Our typical (Non-Seismic) installation above a ceiling is 8-1/2" to center of pipe. This allows us to use a 6" nipple and reducer to recessed heads. This normally requires a 1'-0" Min. space below duct work for elect, lights, sprinkler and support hangers for the duct work, since BOD will require an additional 1" to 3" for supports depending on size of duct
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ron Greenman Sent: Friday, July 31, 2009 10:36 AM To: [email protected] Subject: Re: Renegade HVAC Contractor Garth, Are you in a seismic zone? I've found high to be better when you have a lot of bracing but I'd otherwise agree with your comments. On Fri, Jul 31, 2009 at 9:29 AM, Garth W. Warren<[email protected]> wrote: > Everyone on here seems to be suggesting hanging high. From a > different perspective I always requested a 6" or 8" clear space > directly above the space required by the electrician for light and > their installation (usually > 6 to 8"). _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)