Labs are covered by NFPA 45.  See table 2-2(A) in the 2002 edition for
maximum amounts of flammable or combistible liquids.

On Mon, Sep 14, 2009 at 3:24 PM, <[email protected]> wrote:

> The lab would probably be classified by building code as a B occupancy and
> with that, exempt from sprinklers under most conditions.  However depending
> on the chemicals used and specifically the quantities it could become and
> "H" occupancy.
>
> NFPA 13 would be appropriate in most cases but you cold be driven to NFPA
> 30 depending on quantities of materials.  Someone needs to look at the
> quantities of materials used and stored within the building and do a
> Hazards/Code analysis.
>
> The only thing about mixing up design criteria for small spaces like
> restrooms is, are you really going to be able to get 0.10 for a few heads in
> a rest room when the adjacent areas could be 0.20 or 0.30?
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Greg McGahan
> Sent: Monday, September 14, 2009 3:15 PM
> To: [email protected]
> Subject: Laborotories
>
> Just checking in with this one...
>
> If you have a lab in a stand alone building - regardless of class - all of
> the other rooms, etc should still be able to be protected per normal NFPA 13
> requirements, correct? Bathrooms would be Light Hazard and so forth? We have
> an engineer that is not sure. And I am just making sure I am correct and
> that a lab is no different than any other mixed occupancy classification
> like retail, etc..
>
> Thanks,
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection
> 1160 McKenzie Road
> P.O. Box 877
> Cantonment, Florida 32533
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to