Playing from memory (always a dangerous thing), building design for  
labs is heavy influenced by separation considerations which also  
directly impact the sprinkler design.  Make sure the IBC and NFPA 45  
requirements are covered while you're doing the consult work for the  
engineer.  Hearing the words "I'm unsure" doesn't warrant a lot of  
confidence though I'm sure that was uttered in the presence of the  
owner.

This does make me wonder why aren't you just following the spec  
(though it MAY be overkill, it's not wrong).

A more pertinent question might be, I have a spec calling the whole  
building OH but parts are definitely LH.  Am I still required to use  
QR in portions  of the building?  It would be a better question if the  
spec said EH (since who wouldn't use QR in the OH  so as to get the  
reduction) but the underlying principle still makes it a valid question.

Roland

On Sep 14, 2009, at 12:15 PM, Greg McGahan wrote:

> Just checking in with this one...
>
> If you have a lab in a stand alone building - regardless of class -  
> all of the other rooms, etc should still be able to be protected per  
> normal NFPA 13 requirements, correct? Bathrooms would be Light  
> Hazard and so forth? We have an engineer that is not sure. And I am  
> just making sure I am correct and that a lab is no different than  
> any other mixed occupancy classification like retail, etc..
>
> Thanks,
>
> Greg McGahan
> Operations Manager
>
> Living Water Fire Protection
> 1160 McKenzie Road
> P.O. Box 877
> Cantonment, Florida 32533
> (850) 937.1850 | Fax (850) 937.1852 | Cell (850) 554.3231
> [email protected]
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to