Yes, heres the original email;

From: John Drucker [mailto:[email protected]] 
Sent: Tuesday, April 21, 2009 7:49 AM
To: '[email protected]'
Subject: RE: antifreeze combustibility?

Members,

An incident related to antifreeze occurred at the WindanSea, Highlands, NJ
where a sprinkler system containing antifreeze discharged in proximity to a
unit heater. The atomized liquid was ignited by the unit heater and
occupants burned from the fire that resulted. 

CASE: Rohmer Vs. Windansea, Allied Fire and Safety Equipment and Infared
Dynamics, Inc. 

TYPE OF LOSS: Fire involving sprinkler system anti-freeze solution

NRG REFERENCE NO.: 1590-1-05 DATE: 1/12/06 COURT: Superior Court of New
Jersey, Law Division 

Morris County, Docket No. MNSL-329-03 REPRESENTING: Plaintiff ATTORNEY FOR
PLAINTIFF: Duane Morris LLP 

Hamilton, NJ Michael W. O'Hara, Esquire ATTORNEY FOR 

DEFENDANT WINDANSEA: Bolan, Jahnsen, Ball & Reardon Shrewsbury, NJ Vicki
Shea-Connolly, Esquire 

ATTORNEY FOR DEFENDANT ALLIED FIRE AND SAFETY EQUIPMENT: Marshall, Dennehey,
Warner, Coleman & 

Goggin Cherry Hill, NJ John Osorio, Esquire 

ATTORNEY FOR DEFENDANT INFARED DYNAMICS: James D. Butler, P.A. 

Jersey City, NJ Warren C. Farrell, Esquire

Hope this helps;

John Drucker
Fire Protection Subcode Official
Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, October 22, 2009 5:02 PM
To: [email protected]
Subject: Re: Report: Antifreeze sprinkler system may have contributed to
fatal explosion

Didn't we have this discussion on the Forum a 
while back about 100% anti-freeze solution vs. anti-freeze/water mixtures?



At 04:44 PM 10/22/2009, you wrote:
>Why is there an antifreeze system inside a building? Not knowing what was
>used in the system, here is the info from the ethylene glycol MSDS:
>
>Section 5: Fire and Explosion Data
>
>Flammability of the Product: May be combustible at high temperature.
>
>Auto-Ignition Temperature: 398°C (748.4°F)
>
>Flash Points: CLOSED CUP: 111°C (231.8°F). (Tagliabue.)
>
>Flammable Limits: LOWER: 3.2%
>
>Products of Combustion: These products are carbon oxides (CO, CO2).
>
>Fire Hazards in Presence of Various Substances:
>Slightly flammable to flammable in presence of open flames and sparks, of
>heat.
>Non-flammable in presence of shocks.
>
>This looks like antifreeze systems need to be investigated by NIST to
>determine the dangers.
>
>Thank You
>
>Rahe Loftin, P.E.
>Region 7 - GSA
>Office - 817-978-7299
>Fax - 817-978-8644
>Cell - 817-371-3102
>
>
>
>
>
>              "Richard Mote"
>              <rich...@rowespri                                          To
>              nkler.com>                <[email protected]>
>              Sent by:                                                   cc
>              sprinklerforum-bo
>              un...@firesprinkl                                     Subject
>              er.org                    Report: Antifreeze sprinkler system
>                                        may have contributed to fatal
>                                        explosion
>              10/22/2009 03:18
>              PM
>
>
>              Please respond to
>              sprinklerfo...@fi
>              resprinkler.org;
>              Please respond to
>                Richard Mote
>              <rich...@rowespri
>                 nkler.com>
>
>
>
>
>
>
>Say What?
>
>http://www.sierrasun.com/article/20091020/NEWS/910169995/1066&ParentProfile
=1051
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to