Roland - >From the IRC 2006
Under Section R317 Dwelling Unit Seperation R317.2 Townhouses. Each townhouse shall be considered a separate building and shall be separated by fire--resistance-rated wall assemblies meeting the requirements of Section R302 for exterior walls. Exception: A common 2-hour fire-resistance-rated wall is permitted for townhouses if such walls do not contain plumbing or mechanical equipment, ducts or vents in the cavity of the common wall. Electrical installations shall be installed in accordance with Chapters 33 through 42. Penetrations of electrical outlet boxes shall be in accordance with Section R317.3. R317.2.1 Continuity. The fire-resistance-rated wall or assembly separating townhouses shall be continuous from the foundation to the underside of the roof sheathing, deck or slab. The fire-resistance rating shall extend the full length of the wall or assembly, including wall extensions through and separating attached enclosed accessory structures. Ken Holsopple >Roland wrote: >I don't think townhouses are required to have FIRE WALLS. John - what >do say???? Have to suspect your 100 to 200 year old masonary walls >may do the job. >Roland _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)