Hmmm,

2006 IRC

R317.2 Townhouses. Each townhouse shall be considered a separate
building and shall be separated by fire--resistance-rated wall
assemblies meeting the requirements of Section R302 for exterior walls.

R302.1 Exterior walls. Construction, projections, openings and
penetrations of exterior walls of dwellings and accessory buildings
shall comply with Table R302.1.

TABLE R302.1 Exterior Walls - Walls (Fire-resistance rated) 1 hour with
exposure from both sides 0 feet

So that allows zero separation when the exterior walls of each townhouse
have a one hour fire resistance rating. Essentially two independent
buildings with one hour rated exterior walls pushed up against each
other. Sounds to me like 2 hours of fire resistance. Also just what is
an exterior wall ?. 

EXTERIOR WALL. An above-grade wall that defines the exterior boundaries
of a building. Includes between-floor spandrels, peripheral edges of
floors, roof and basement knee walls, dormer walls, gable end walls,
walls enclosing a mansard roof and basement walls with an average
below-grade wall area that is less than 50 percent of the total opaque
and nonopaque area of that enclosing side.

So an exterior wall defines the exterior boundaries of a building,
emphasis on building.  I'll take that, if one collapses the other
remains standing since they are independent of each other.

Ok so lets look at the exception;

Exception: A common 2-hour fire-resistance-rated wall is permitted for
townhouses if such walls do not contain plumbing or mechanical 
equipment, ducts or vents in the cavity of the common wall. Electrical
installations shall be installed in accordance with Chapters 33 through
42.Penetrations of electrical outlet boxes shall be in accordance with
Section R317.3.

R317.2.1 Continuity. The fire-resistance-rated wall or assembly
separating townhouses shall be continuous from the foundation to the
underside of the roof sheathing, deck or slab. The fire-resistance
rating shall extend the full length of the wall or assembly, including
wall extensions through and separating attached enclosed accessory
structures.

So just how do we build a common 2 hour fire resistance rated wall,
remember it has to be common and not part of one building or the other.

The H-Stud Area Separation Wall (ASW) system offers the advantages of
constructing common walls with fire resistive protection and noise
reduction between neighboring housing units. This lightweight, non-load
bearing 2-hour fire rated drywall assembly was developed as a vertical
fire protection that provides STC sound ratings up to 60-64 between
common wall units in wood framed townhouses and apartment complexes up
to four stories (44') in height with the assumption all floor heights
are of normal elevation. This system was designed as a fire barrier
between adjacent dwelling units allowing for the falling away of
construction on the fireexposed side without collapse of the entire
wall. This is accomplished with the aluminum breakaway clips that attach
the ASW to adjacent wood framing. When one side of the system is exposed
to fire, the clips soften, break away and allow the wall on the fire
side to give way. The aluminum breakaway clips on the non-fire side will
remain intact, holding the ASW in place as a barrier to protect
neighboring spaces.

While the term "firewall" isnt used it sure looks, walks and quacks like
one.  If anyone wants the assembly detail;

http://www.nationalgypsum.com/submittal/09%2021%2016.33-23.pdf
http://www.americangypsum.com/pdfs/AreaSeparationWallSystem.pdf

PS, No endorsement of any kind is made or intended, used for
demonstration purposes only.

Hope that helps,

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
New Jersey 






-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Thursday, November 05, 2009 3:39 PM
To: [email protected]
Subject: Re: Townhouse or Apartment Building

There you go - just a rated partition and not a fire wall.

I'll either have to call Ken - John Jr or just reference having the code
boys to get'er done

Roland

On Nov 5, 2009, at 12:25 PM, Ken Holsopple (forum) wrote:

> Roland -
>
>> From the IRC 2006
>
> Under Section R317 Dwelling Unit Seperation
>
> R317.2 Townhouses.
> Each townhouse shall be considered a separate building and shall be
> separated by fire--resistance-rated wall assemblies meeting the
> requirements of Section R302 for exterior walls.
>
> Exception: A common 2-hour fire-resistance-rated wall is permitted for
> townhouses if such walls do not contain plumbing or mechanical
> equipment, ducts or vents in the cavity of the common wall. Electrical
> installations shall be installed in accordance with Chapters 33
> through 42.
> Penetrations
> of electrical outlet boxes shall be in accordance with Section R317.3.
>
> R317.2.1 Continuity.
> The fire-resistance-rated wall or assembly separating townhouses shall
> be continuous from the foundation to the underside of the roof
> sheathing, deck or slab. The fire-resistance rating shall extend the
> full length of the wall or assembly, including wall extensions through
> and separating attached enclosed accessory structures.
>
> Ken Holsopple

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)




CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to